The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 164 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96186 - 11/09/05 09:37 AM Service Panel Height
skingusmc Offline
Member

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
All -

What is the maximum height that a service panel (main cm panel)in a home can be?

I "seem" to remember (the second thing to go) that it is 6' with an exception that lets you go to 6.5'.

Am I having a "senior moment" or is it out there and I just can't find it?

A reference would certainly be great.

Thanks
Steve
_________________________
Thanks
Steve

Top
2017 / 2014 NEC & Related Books and Study Guides
#96187 - 11/09/05 09:46 AM Re: Service Panel Height
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.

Now the only question becomes is the highest breaker in the panel being used as a switch.
--
Tom Horne

[This message has been edited by tdhorne (edited 11-09-2005).]
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#96188 - 11/09/05 07:34 PM Re: Service Panel Height
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
"Now the only question becomes is the highest breaker in the panel being used as a switch."

It is if it's the main service disconnect, meant to be manually operated.