The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96186 - 11/09/05 09:37 AM Service Panel Height
skingusmc Offline
Member

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
All -

What is the maximum height that a service panel (main cm panel)in a home can be?

I "seem" to remember (the second thing to go) that it is 6' with an exception that lets you go to 6.5'.

Am I having a "senior moment" or is it out there and I just can't find it?

A reference would certainly be great.

Thanks
Steve
_________________________
Thanks
Steve

Top
2014 / 2011 NEC & Related Books and Study Guides
#96187 - 11/09/05 09:46 AM Re: Service Panel Height
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.

Now the only question becomes is the highest breaker in the panel being used as a switch.
--
Tom Horne

[This message has been edited by tdhorne (edited 11-09-2005).]
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#96188 - 11/09/05 07:34 PM Re: Service Panel Height
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
"Now the only question becomes is the highest breaker in the panel being used as a switch."

It is if it's the main service disconnect, meant to be manually operated.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com