The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 268 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96186 - 11/09/05 09:37 AM Service Panel Height
skingusmc Offline

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
All -

What is the maximum height that a service panel (main cm panel)in a home can be?

I "seem" to remember (the second thing to go) that it is 6' with an exception that lets you go to 6.5'.

Am I having a "senior moment" or is it out there and I just can't find it?

A reference would certainly be great.


2014 / 2011 NEC & Related Books and Study Guides
#96187 - 11/09/05 09:46 AM Re: Service Panel Height
tdhorne Offline

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.

Now the only question becomes is the highest breaker in the panel being used as a switch.
Tom Horne

[This message has been edited by tdhorne (edited 11-09-2005).]
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#96188 - 11/09/05 07:34 PM Re: Service Panel Height
Larry Fine Offline

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
"Now the only question becomes is the highest breaker in the panel being used as a switch."

It is if it's the main service disconnect, meant to be manually operated.
Larry Fine
Fine Electric Co.