#96171 - 11/07/05 07:43 AM Bonding water pipe
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
Do you think in my situation that my copper water line is bonded properly? The unistrut which carries the copper water line is bolted to the building steel. The building steel is bonded to the egc. Would that be a sufficient bond? In the building I'm working on the plumber has changed over from pvc to copper all over the place. So, I'm just tring to figure out everywhere I need to run a bond wire. {It's a industrial cemical building}
Top
2017 / 2014 NEC & Related Books and Study Guides
#96172 - 11/07/05 08:19 AM Re: Bonding water pipe
raider1 Offline
Member
Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
Take a look a 205.104 NEC 2005.

I think that to be code compliant you would need to use a water pipe clamp and install a bonding jumper to the building steel installed in accordance with 250.64(A)(B)(E)

JMHO, Chris
Top
#96173 - 11/08/05 02:13 PM Re: Bonding water pipe
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
That plumber better have his work cleared by the engineers. Many, many chemicals will tear up copper. I suspect that is why the original installation was in plastic.

Don't be too surprised if the plumber gets spanked. Who approved this dramatic change?
_________________________
Tesla
Top
#96174 - 11/08/05 03:33 PM Re: Bonding water pipe
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
He passed his final inspection. I asked the same question. Why am I using pvc coated ridged when he is using copper. It's water treatment cemicals, very corrosive.
Top
#96175 - 11/08/05 05:45 PM Re: Bonding water pipe
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
The copper water lines should have isolation straps at the strut so there is no metal to metal contact. If the copper lines are held with standard strut clamps both the plumber and the plumbing inspector are not very bright.

Curt
_________________________
Curt Swartz
Top
#96176 - 11/19/05 09:17 AM Re: Bonding water pipe
Paul O'Connell Offline
Member
Registered: 07/02/05
Posts: 56
Loc: Allen Park, Mi. USA
Two key words in bonding requirements.

1. Perminent.
2. Approved fittings.
Top
#96177 - 11/19/05 12:14 PM Re: Bonding water pipe
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
It may be that the particular chemicals used do not react with copper, but do react with steel. Or, the copper pipes may be slated to be painted or covered later. The inspector may not be aware of the corrosive qualities, but the designing engineer should.

The code (250.104(A)(1)) requires water piping SYSTEMS to be bonded to the grounding electrode system, either to the GEC, to the service neutral bus or to a grounding electrode used (such as building steel)

If you have isolated sections of water pipe, you may not have to bond all of them together. This call, as to when an isolated pipe becomes long enough to be considered a system, lies with the AHJ. To be safe bond them all together, and to the grounding system.

Like Paul said, make your connections permanent and use approved fittings designed for the purpose and conditions of use.
_________________________
Earl
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals