#96031 - 10/31/05 06:05 AM Return air wiring method
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What are your thoughts about using a cable Listed as CL2R in the return air joist space of a residential occupancy? Is this acceptable by inspectors or should this be CL2P?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#96032 - 10/31/05 10:00 AM Re: Return air wiring method
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Vote me "plenum".
Riser rating only has to do with flame spread, not toxicity of the smoke as far as I understand.
_________________________
Greg Fretwell
Top
#96033 - 10/31/05 04:22 PM Re: Return air wiring method
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Is the joist space in a residential occupancy considered to be a plenum?
_________________________
George Little
Top
#96034 - 10/31/05 05:24 PM Re: Return air wiring method
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I suppose it would all depend on how you ran the wire. Is it passing through at a 90 or running with the bay
_________________________
Greg Fretwell
Top
#96035 - 10/31/05 06:08 PM Re: Return air wiring method
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

Here in some of my towns the building or fire inspector will fail a job if wire, RX or other, is run through any ductwork in a resi bldg. There is one job here I was looking at and th tin knockers "Panned" a whole main girder. and when they did that, they enclosed not only wires, but there was a large waste line. "Panning" is when the tin knockers put a flat piece of tin across the bottom of your 2 X 10's and they use that area to move air instead of using a piece of ductwork itself.
Top
#96036 - 10/31/05 07:17 PM Re: Return air wiring method
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think the answer is in 300.22(C)ex
Quote:
Exception: This section shall not apply to the joist or stud spaces of dwelling units where the wiring passes through such spaces perpendicular to the long dimension of such spaces.


When I first read George's note I was thinking about wires running down the stud bay <the riser ref in CL2R>.
If they simply cross the bay it is probably OK but YMMV with various AHJs
I have seen it go both ways in suspended ceilings and computer floors too.
All IBM interface and power cables after about 1994 were plenum rated (AKA "DP"), tan colored. The blue ones were riser rated and tolerated until we could swap them out but the grey (unrated) ones had to go.

In other than dwellings 725.61(A) would affect low voltage wire, no matter which direction it ran.
Quote:
(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CL2P or CL3P ...


[This message has been edited by gfretwell (edited 10-31-2005).]
_________________________
Greg Fretwell
Top
#96037 - 10/31/05 09:07 PM Re: Return air wiring method
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg nailed it. I was addressing the wiring installed with the air flow and the code reference 725.61(A) talks about cables in plenums, ducts and other space used for environmental air as needing to be Listed and labeled as plenum cable. the other reference is valid if you are installing cables perpendicular to the air flow.
_________________________
George Little
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 64 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals