shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can I use the old 100 amp, 20 circuit main panel as a juction box on a 200amp service upgrade where I will be changing the location of the panel?

I'm moving the panel 4 feet to get the needed working clearance. I'll strip out the guts of the panelboard.

I know I've seen this done before. I want to know if it is code compliant?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#96019 - 10/31/05 04:30 AM Re: Panel -Juction Box
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
It is a box designed for electrical wiring. I consider it OK as long as you can't open the cover by the hinges, and that you consider derating if you run all the circuits in one large conduit between the two.

Sometimes it's a more attractive installation to have some 4X4 junction boxes over the old panel for the short wires, and pull the long ones into the new panel.

Dave
Top
#96020 - 10/31/05 04:03 PM Re: Panel -Juction Box
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Why can't you open the old panel by its hinges?
Top
#96021 - 10/31/05 05:37 PM Re: Panel -Juction Box
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Many inpspectors here will allow a panel to be used as only if you screw the door shut, so wiring isn't exposed throught the breaker KO's. They won't accept breaker KO'seals/blanks as many easily fall out. Some will go as far as to have you write on the panel (Now j-box), "No breakers or fuses inside."
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#96022 - 10/31/05 06:01 PM Re: Panel -Juction Box
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If you could come up with a blank cover for the cabinet it isn't a breaker box anymore.
That would be a cleaner installation.
_________________________
Greg Fretwell
Top
#96023 - 11/02/05 03:08 AM Re: Panel -Juction Box
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Then would that leave a hinge-cover wireway or gutter in the same boat?
I can understand this in the case of a panel that doesn't have any door on it.
The marking is a good idea, and I've screwed many of the doors shut myself.
I just didn't understand the logic behind its being a requirement.
Thanks
Top
#96024 - 11/02/05 08:47 AM Re: Panel -Juction Box
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
I have been reading the code book for 30 years and haven't yet found any requirement to screw the cover shut when turning it into a j-box. Now you could find lots of codes that pertain to other things that could be redily misaplied to this such as listing requirements and protection from physical damage, etc, but it realy is not prohibited in any way.
Top
#96025 - 11/02/05 12:45 PM Re: Panel -Juction Box
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
I don't think it's much of a stretch to consider the gaping hole left by the absence of breakers an "unused opening".

Then Article 110.12 (A) would apply.

Dave
Top
#96026 - 11/02/05 01:40 PM Re: Panel -Juction Box
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
It's interesting that breaker blanks are acceptable when the panel's buses are hot, but not okay when they're dead.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#96027 - 11/02/05 02:16 PM Re: Panel -Juction Box
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
+1 for the idea of a blank cover. I don't know if the OEM make them - it would probably be a job for a local metal fab place - but I think it would be a cleaner look.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals