#95985 - 10/28/05 12:46 PM Wire protection method?
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 178
Loc: nc
Adding a circuit to a heat pump under a mobil home that has been underpinned would it be aceptable to run a shethed cable or would conduit be required?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95986 - 10/28/05 05:30 PM Re: Wire protection method?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
While underpinning may convert the home from "mobile" to "permanent" in the eyes of the tax and zoning folks, it doesn't change a thing in the NEC.

The wire needs to be in pipe.
Top