#95979 - 10/27/05 09:11 AM Conductor Derating 2
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Thsi topic is being discussed in two other threads but here is a different question.
Assume 10 120V circuits each with their own neutral. #12 all in one conduit to a juction box with one ground wire and a ground bus in the junction box. Separate MC from there to the devices, lighting etc.
50% of 25A is 12.5 amps. Does that mean that the branch circuit breaker needs to be less than 12.5 amp? Or just that the connected load can not exceed 12.5 amps?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95980 - 10/27/05 09:28 AM Re: Conductor Derating 2
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Note that for derating based upon number of conductors in a conduit, you get to work from the temperature rating of the wire, even if it is higher than that of the terminations. So you would probably use THHN 90C wire, with an ampacity of 30A, 15A after derating with a 15A breaker.

-Jon
Top
#95981 - 10/27/05 10:13 AM Re: Conductor Derating 2
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Quote:
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Not if the circuit supplies a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
See 240.4(B)(1).
Don
_________________________
Don(resqcapt19)
Top
#95982 - 10/27/05 01:38 PM Re: Conductor Derating 2
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I agree Don, if the circuits are feeding receptacles you looking at 10a circuit breakers.
_________________________
George Little
Top
#95983 - 10/27/05 06:29 PM Re: Conductor Derating 2
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
OK, so for the receptacle circuits we can not go to the next higher size circuit breaker.
But, if the wire is 90C we can use 30 amp which means 15 amp and a 15 amp receptacle?
(regardless of the termination rating?)
Top
#95984 - 10/27/05 07:36 PM Re: Conductor Derating 2
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
If you have a 90° wire (THHN) #12 AWG using it in a ambient of 86° damp or dry location and derate to 15a due to raceway fill, you could feed 15 receptacles and have a 15a overcurrent device protecting it.
_________________________
George Little
Top

Newest Members
Fidellis, gmarsden, Jerryglover87, Dan_Burns, pauldgardner
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:08 AM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (Admin, Fidellis), 132 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 05/03/03
Posts: 1231

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals