The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95979 - 10/27/05 09:11 AM Conductor Derating 2
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Thsi topic is being discussed in two other threads but here is a different question.
Assume 10 120V circuits each with their own neutral. #12 all in one conduit to a juction box with one ground wire and a ground bus in the junction box. Separate MC from there to the devices, lighting etc.
50% of 25A is 12.5 amps. Does that mean that the branch circuit breaker needs to be less than 12.5 amp? Or just that the connected load can not exceed 12.5 amps?

Top
2014 / 2011 NEC & Related Books and Study Guides
#95980 - 10/27/05 09:28 AM Re: Conductor Derating 2
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Note that for derating based upon number of conductors in a conduit, you get to work from the temperature rating of the wire, even if it is higher than that of the terminations. So you would probably use THHN 90C wire, with an ampacity of 30A, 15A after derating with a 15A breaker.

-Jon

Top
#95981 - 10/27/05 10:13 AM Re: Conductor Derating 2
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
 Quote:
The load on each circuit would need to be less than 12.5A, but you could use the next larger standard breaker, eg. a 15A breaker.

Not if the circuit supplies a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
See 240.4(B)(1).
Don
_________________________
Don(resqcapt19)

Top
#95982 - 10/27/05 01:38 PM Re: Conductor Derating 2
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I agree Don, if the circuits are feeding receptacles you looking at 10a circuit breakers.
_________________________
George Little

Top
#95983 - 10/27/05 06:29 PM Re: Conductor Derating 2
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
OK, so for the receptacle circuits we can not go to the next higher size circuit breaker.
But, if the wire is 90C we can use 30 amp which means 15 amp and a 15 amp receptacle?
(regardless of the termination rating?)

Top
#95984 - 10/27/05 07:36 PM Re: Conductor Derating 2
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
If you have a 90┬░ wire (THHN) #12 AWG using it in a ambient of 86┬░ damp or dry location and derate to 15a due to raceway fill, you could feed 15 receptacles and have a 15a overcurrent device protecting it.
_________________________
George Little