The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#95958 - 10/26/05 05:39 PM Service Laterals
Gee Offline
Junior Member

Registered: 10/26/05
Posts: 9
Loc: baton rouge LA, USA
hey guys great site,I might stick around.

but I have an urgent question for now.

I have a 208v, 3 phase, service lateral
(pad mount xformer secondary) feeding a 1600 Main breaker switch board.
In the past the utility company has run the secondarys, now they are requiring the customer to provide them.
The local utility had always undersized them IMO. Now that we must provide them, am I right in assuming that we must size these greater than the service main, in this case 4 sets of 500 MCM cu. ?

The project engineer tells me to run 4 sets of 350 MCM, however it is my opinion that this does not meet the NEC and 500 MCM conductors are required.

I hope I was clear with my question. and thanks in advance..

Top
2014 / 2011 NEC & Related Books and Study Guides
#95959 - 10/26/05 07:22 PM Re: Service Laterals
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Even 4 sets of 500kcmil is not adequate. 500kcmil is only rated for 380A at 75C (the rating of the terminations in the service gear). Above 800A you are not permitted to round up.

Top
#95960 - 10/26/05 08:23 PM Re: Service Laterals
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
JBD is right again. 4 sets of 500 kcm is good for 1520 amps. You will need 4 sets of 600 kcm at 420 amps for a total of 1680 amps as per 240.4C.

Top
#95961 - 10/27/05 03:04 AM Re: Service Laterals
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Is there any chance that these are still _specificed_ by the POCO using their sizing rules, even though they are to be installed by the customer's electrician?

-Jon

Top
#95962 - 10/27/05 06:55 AM Re: Service Laterals
Gee Offline
Junior Member

Registered: 10/26/05
Posts: 9
Loc: baton rouge LA, USA
Correct you are about 600 MCM. I'm not doing my own math here.
The laterals were not specified by the power co. The project engineer specified the laterals on plans. Later admitting that they resized the MDP during the design and forgot the increase the service laterals.
The engineers later asked for change order pricing to increase to 4 sets #500MCM. ( thats where I got the #500). Now the owner has said he will not approve any additional funds. So the engineer has stated my change order request will not be approved. I am concerned about my liabilty in this issue due to not meeting the NEC. This project has turned very bad due to some other issues with design oh which I am taking a beating due to the engineer's faults. I really do not want to butt heads with the engineer and harm a relationship for future projects, But I do not think I have a choice. Anyone else have any ideas ?

Top
#95963 - 10/27/05 07:43 AM Re: Service Laterals
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Gee,
 Quote:
the project engineer specified the laterals on plans. Later admitting that they resized the MDP during the design and forgot the increase the service laterals.
The engineers later asked for change order pricing to increase to 4 sets #500MCM. thats where I got the #500).
the engineer admits his mistake here and does the right thing by asking you to submit a change order.

 Quote:
Now the owner has said he will not approve any additional funds. So the engineer has stated my change order request will not be approved.
So now he is in effect saying, "my mistake will come out of your pocket, not mine".

The engineer has Errors and Omissions insurance that would cover his mistake if he can not come to an agreement with the owner.

Whatever happens you should not entertain the thought of making the correction at your expense even if this strains your relationship with this engineer.

Roger

Top
#95964 - 10/27/05 09:05 AM Re: Service Laterals
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
What is the actual calculated load? If it is 1400 amps or less, install a second service disconnect and the 4 sets of 350.
Don
_________________________
Don(resqcapt19)

Top
#95965 - 10/27/05 01:22 PM Re: Service Laterals
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Don has a great idea here.

You could go with two 800 amp service disconnects eliminating the need for GFP and allowing the use of the 350s or 500s depending on the calculated load.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#95966 - 10/27/05 01:35 PM Re: Service Laterals
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Watch out for 240.21(C)(4). This would have you terminating in a single overcurrent device.
_________________________
George Little

Top
#95967 - 10/27/05 01:54 PM Re: Service Laterals
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
240.21(C)(4) does not apply to service conductors.

Check out 240.21(D)

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top