The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 60 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95955 - 10/24/05 04:12 PM 310.15(a)(6)
gserve Offline
Member

Registered: 03/11/03
Posts: 92
When wiring a garage on residential property and feeding it from a separate feeder off of the main service panel mounted on a pole can I use this exception for the feeders or do they have to be per 310.15 table? In other words feeders to home as per 310.15(a)(6)and feeders to garage per 310.15(a)(6).

Top
2017 / 2014 NEC & Related Books and Study Guides
#95956 - 10/24/05 04:47 PM Re: 310.15(a)(6)
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Read the article closely,

Quote:
120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s). The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met.


Roger

Top
#95957 - 11/09/05 10:04 AM Re: 310.15(a)(6)
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
IMUHO you can not use the residential service table for separate service conductors to a detached garage.

In the completely different case of the service conductors for a detached home that first runs to service equipment located in a detached garage you can only use the residential service cconductor sizing between the detached garage and the house but not between the service point and the service equipment that is located in a detached garage.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison