#95933 - 10/23/05 09:23 AM conductor derating
shkrg24 Offline
Junior Member
Registered: 10/22/05
Posts: 1
I need to run a 1" cond. from a 120/208V 3ph panel to an area of a bldg. to feed 9ea. 20A recep. circuits in clinical exam rooms. If I pull 3, 3ph and neutral sets with 1 ground, and use #10 wire to the first device on each circuit, does that cover the de-rating issues, or are there other factors to consider?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95934 - 10/23/05 09:36 AM Re: conductor derating
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Funny I just posted a topic with this same question....
http://electrical-contractor.net/ubb/Forum2/HTML/002340.html


[This message has been edited by e57 (edited 10-23-2005).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#95935 - 10/23/05 09:38 AM Re: conductor derating
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If you run 3 - 3 phase multiwire branch circuits you will have 9 current carrying conductors.

Assuming you use 90 C conductors you can use 12 AWG all the way for these 20 amp circuits.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95936 - 10/24/05 05:09 PM Re: conductor derating
boggerbutt2454 Offline
Member
Registered: 02/27/05
Posts: 44
Loc: Concord NC USA
iwire
9 recept. circuits is 12 current carrying conductors as you forgot the 3 neutrals as well as the 9 ungrounded conductors.
10-20 conductors means your derate factor is 50%or 15 amps. You need to add another conduit. 240.4(D) #10 30 amps.
Top
#95937 - 10/24/05 05:17 PM Re: conductor derating
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
iwire
9 recept. circuits is 12 current carrying conductors as you forgot the 3 neutrals as well as the 9 ungrounded conductors


The neutrals are not current carrying conductors unless the major potion of the load consists of non-linear loads.

IMO the receptacles described are likely to be feeding linear loads.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95938 - 10/24/05 05:37 PM Re: conductor derating
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Bob as you mentioned in the other post of simular issue "Major Portion" is pretty broad.... 310.15(4) doesn't say anything about "Connected load", but dealing with recepticals you'll never know what they'll throw on down the line. Or for that matter what type of load balance you'll end up with.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#95939 - 10/25/05 02:09 AM Re: conductor derating
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The 'balance' is entirely irrelevant, the neutral may end up carrying 20 amps but it is still not a '"current carrying conductor" in regards to derating.

As far as the non-linear load issue that is up to the installer and inspector to determine.

As I said IMO the described receptacles "9ea. 20A recep. circuits in clinical exam rooms." Do not sound to me like the major potion of the load will be non-linear.

Your always free to count the neutral as a CCC if you want to, generally I do not.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95940 - 10/27/05 06:44 PM Re: conductor derating
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
I agree with iwire. On the other hand if you are feeding non-linear loads I do not believe you should be using a common neutral anyway. In that case (separate neutral) the neutral would be current carrying.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals