I was taking one of my classes for my 34 hr. CEUs today, and a question came up that had the class and instructor stumped.

One of the guys was red-tagged by an inspector on a service installation using PVC conduit on the driveway side of a house. He used Sch. 80 pipe, with an LB below the meter pan to penetrate the wall into the panel.

Inspector claimed that the LB was subject to damage because it wasn't Schedule 80 rated.

Are heavy schedule PVC conduit bodies even manufactured?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95928 - 10/23/05 08:36 AM Re: PVC conduit body schedule?
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
I don't know, but he could go with metal to comply.

Dave
Top
#95929 - 10/23/05 10:39 AM Re: PVC conduit body schedule?
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
You need to contact the manufacturer. Most claim that the reinforcing in the LBs creates a strength comparable to Sch. 80 conduit.
In my experience I have seen Sch. 40 conduit fail but have yet to see an LB broken.
Be carfull about using a metal LB if it is connected to PVC at both ends and has service conductors, because you now have to bond the LB.
Alan--Inspector.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#95930 - 10/30/05 05:06 PM Re: PVC conduit body schedule?
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I did a service like this this week. I used schedule 80 on the load side from the meter to the disco and lb'ed into a sweep and then into the panel. What I didn't do, though, was show the lettering on the schedule 80 to prove to the inspector that it was used. Do you think the inspector will fail the job?
Top
#95931 - 10/30/05 05:11 PM Re: PVC conduit body schedule?
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
ShockMe77, if you used a PVC LB, pull the cover off the LB, the end of the pipe is probably visible and the wall thickness can be seen.

steve
Top
#95932 - 10/31/05 06:07 PM Re: PVC conduit body schedule?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Can't say I ever seen/found a Sch 80 condulet, MA/FA/Cplg, etc.

Had the same thought, "should be same sch as conduit???".......called Carlon, had a chuckle. Guy said something to the effect of Alan Nadon's comments.

John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals