#95897 - 10/18/05 11:33 AM Ground Rod
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Can somene help me with locating the Section number in the '02 NEC that says that an optional Ground Rod at a light pole for instance, does not need to meet the <25 ohms called for like it is for a System Grounding Electrode? I know it's there somewhere but I can't find it.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#95898 - 10/18/05 01:27 PM Re: Ground Rod
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Quote:
250.54 Supplementary Grounding Electrodes.
Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.

Don
_________________________
Don(resqcapt19)
Top
#95899 - 10/18/05 01:49 PM Re: Ground Rod
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Thanks Don. I thought I was losing it because I couldn't find that code reference.
_________________________
George Little
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals