#95875 - 10/16/05 08:36 AM Disconnect Mounting
wire dummy Offline
Junior Member
Registered: 10/12/05
Posts: 4
Loc: Ohio
I need to mount a 100a switch over an existing single gang box in a wall.The conduit is 1.25 coming into the box.I have never mounted one over a box before.I thought I could just nipple it and be done. Any code issues or helpful hints would be appreciated.
Top
2017 / 2014 NEC & Related Books and Study Guides
#95876 - 10/16/05 09:21 AM Re: Disconnect Mounting
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
I'd need a lot more info to respond to this, and a pic wouldn't hurt.

Is this an abandoned box, or are any wires in the box to enter the disconnect? I can't imagine 100-amps worth of conductors fitting a single-gang box.

If I had to venture a guess now, I'd say to mount an extension box over the existing box, mount the disconnect to one side, and nipple between them.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#95877 - 10/16/05 09:40 AM Re: Disconnect Mounting
wire dummy Offline
Junior Member
Registered: 10/12/05
Posts: 4
Loc: Ohio
Sorry,I see how I needed to be more clearer.There is an empty 1.25 coming into a 4 11/16 box with a single gang plaster ring on it.I need a 70 amp circuit there with a disconnect.There is sheetrock over the box.Thanks in advance.
Top
#95878 - 10/16/05 10:38 AM Re: Disconnect Mounting
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
Access to the box in the wall is an issue. I wouldnt consider needing to remove a disconnect to access a box as accessible. Larry's suggestion is how I do it. An extension box then go to the disconnect.
Top
#95879 - 10/17/05 03:32 PM Re: Disconnect Mounting
wire dummy Offline
Junior Member
Registered: 10/12/05
Posts: 4
Loc: Ohio
I see your point.But,could I mount it over the plaster ring? Is this a code requirement?The wires would pass thru the box to the disconnect.I am more concerned with the code issue more than the convienance of mounting it.Thanks again.
Top
#95880 - 10/17/05 06:25 PM Re: Disconnect Mounting
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
No, I don't think that you could not mount the disconnect over the box and remain code compliant. You would need to maintain accessibility to the box beneath without removing the disconnect. I don't think there would be room enough in the disconnect to cut a 2-1/4 by 4 inch hole to get that access, nor would the listing allow you to modify the box that much. Is it possible to open the wall enough to remove the box, attach an offset bend, and enter the disconnect directly?
_________________________
Earl
Top
#95881 - 10/18/05 06:12 PM Re: Disconnect Mounting
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Maybe I've been missing something in this discussion, but IF there are no splices or connections of any kind in the box (i.e., the wire simply passes through the box on its way to a bushing on the rear of the disconnect), I don't see any problem at all.

Even if new conductors needed to be pulled through at a later time, I would think the box itself would allow enough bend radii to get 'em in.

Thoughts?
_________________________
Stupid should be painful.
Top
#95882 - 10/19/05 04:35 AM Re: Disconnect Mounting
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
The code doesnt make an exception for a junction box that has splices or not. All junction boxes must be accessable.

Even so, What about your ground wire bonding both boxes, theres a splice for you.
Top
#95883 - 10/19/05 08:35 AM Re: Disconnect Mounting
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Is the disconnect part of "the building finish"?

Quote:
Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
_________________________
Greg Fretwell
Top
#95884 - 10/19/05 01:00 PM Re: Disconnect Mounting
wire dummy Offline
Junior Member
Registered: 10/12/05
Posts: 4
Loc: Ohio
Yeah,that is kinda my question/quandry.Is the disco considered the building?I also wouldn't splice the ground,just wrap the wire around the grd screw then go to disco(still a termination?).I am not looking to get around the code,just looking for some insight into the code issues.I have done similar installs on A/C units,but they are accessible.Thanks for the replies.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals