#95819 - 10/09/05 11:05 AM Mutiple Services
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Her's a question, think about a strip mall with 6 stores. There is a main service pipe which runs into a trough. There is 6 meters all nippled off of the trough with the service cable (SEU Type)going into each store. Inside of each store is a service panel with a main breaker. Considering all of the wire sizes is correct and all of the grounding conductors are correct. The question comes, Can you connect the neutrals and the #6 exterior grounding conductor and the interior grounding conductor (that goes to the interior water pipe and is sized as per the service)inside of the trough? Can they all be connected with a split bolt connector? Or can they all be connected to a terminal bar inside of the trough?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95820 - 10/09/05 01:01 PM Re: Mutiple Services
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I think what you are discribing is a single service. maybe you could look at 250.64(D). If you agree then the GEC must be unspliced and the taps can be with split bolts if you'd like.
_________________________
George Little
Top
#95821 - 10/09/05 01:19 PM Re: Mutiple Services
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Look also at 230.40 Exception No.1 and see if that fits what I said about one service.
_________________________
George Little
Top
#95822 - 10/09/05 06:23 PM Re: Mutiple Services
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
When I saw guys do things like this they used the "X" hole Ilsco or similar tap and I was OK with it. (a virtual terminal bar IMHO)
I agree with George, If the GEC is continuous and the neutrals tap off with split bolts it is still OK.
_________________________
Greg Fretwell
Top
#95823 - 10/10/05 06:46 AM Re: Mutiple Services
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
George and Greg,

Thank you for the replies, however I think the question that the EC was trying to ask me, Is it OK to make the connection between the neutrals and GEC in the trough, or do you have to bring the GEC inside to each service panel through out the whole strip mall? BTW, we are still using the 2002 NEC,(I haven't even opened the 2005 yet.)
We will assume that the GEC is unspliced, but what about accessibility? If the POCO locks the trough is it still accessible? I think this was also one of his concerns.
Top
#95824 - 10/10/05 09:19 AM Re: Mutiple Services
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They consider the inside of the meter can "accessible" (for the GEC) here. I assume other AHJs could have another opinion.
_________________________
Greg Fretwell
Top
#95825 - 10/11/05 05:11 PM Re: Mutiple Services
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

Well that is one of the questions the EC asked me. Would I accept the meter pan ( Or in this case a trough) that can be locked by the Poco, "Accessible"? My first thought was, No. But on second thought the code doesn't say "Readily Accessible". SO, is the inside of a meter pan (or trough)"Accessible"? Well maybe, yes.
Top
#95826 - 10/11/05 06:46 PM Re: Mutiple Services
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I suppose it really depends on your PoCo. Around here FPL is OK with a licensed contractor cutting a seal if they have a reasonable story. I did it as a homeowner with a permit.
They told me I could have also done it with a "bad main breaker" story or a "tighten up the neutral/ground) story if I said I was a contractor.

I do have a way of getting information out of the girls on the phone tho.
_________________________
Greg Fretwell
Top
#95827 - 10/12/05 05:11 PM Re: Mutiple Services
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

Gee, I have heard that you were the Don Johnson of Fort Meyers there in Fla.. I think it was the Wiz or th Sheriff who told me that!
How did you make out with the hurricanes this year?
Caper
Top
#95828 - 10/12/05 07:58 PM Re: Mutiple Services
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
This year hurricanes were nothing on this coast.
We had a couple go 100 miles south of us but no big deal.
It has been raining a lot so Judy is having a time getting her footers poured but other than that she is rolling right along. Since she started her new community in Feb she has 76 out of the ground and 18 are in final trim ... without water or power. Prairie building!
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals