The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 04:10 PM
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95817 - 10/08/05 09:28 AM 250.146 Connecting Receptacle Grounding Terminal To Box
ShockMe77 Offline

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Hi, I was just curious as to why this code pertains to receptacles and not to switches. Or does it and I just haven't found it? I believe a ground fault could occur to a 4x4 switch cover plate just as easily as it could to a receptacle cover.


2014 / 2011 NEC & Related Books and Study Guides
#95818 - 10/08/05 09:36 AM Re: 250.146 Connecting Receptacle Grounding Terminal To Box
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
404.9 Provisions for General-Use Snap Switches.

(B) Grounding. Snap switches, including dimmer and similar control switches, shall be effectively grounded and shall provide a means to ground metal faceplates, whether or not a metal faceplate is installed. Snap switches shall be considered effectively grounded if either of the following conditions is met.

(1)The switch is mounted with metal screws to a metal box or to a nonmetallic box with integral means for grounding devices.

(2)An equipment grounding conductor or equipment bonding jumper is connected to an equipment grounding termination of the snap switch.

Exception to (B): Where no grounding means exists within the snap-switch enclosure or where the wiring method does not include or provide an equipment ground, a snap switch without a grounding connection shall be permitted for replacement purposes only. A snap switch wired under the provisions of this exception and located within reach of earth, grade conducting floors, or other conducting surfaces shall be provided with a faceplate of nonconducting, noncombustible material.

[This message has been edited by iwire (edited 10-08-2005).]