#95817 - 10/08/05 09:28 AM 250.146 Connecting Receptacle Grounding Terminal To Box
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Hi, I was just curious as to why this code pertains to receptacles and not to switches. Or does it and I just haven't found it? I believe a ground fault could occur to a 4x4 switch cover plate just as easily as it could to a receptacle cover.

Thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95818 - 10/08/05 09:36 AM Re: 250.146 Connecting Receptacle Grounding Terminal To Box
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
404.9 Provisions for General-Use Snap Switches.

(B) Grounding. Snap switches, including dimmer and similar control switches, shall be effectively grounded and shall provide a means to ground metal faceplates, whether or not a metal faceplate is installed. Snap switches shall be considered effectively grounded if either of the following conditions is met.

(1)The switch is mounted with metal screws to a metal box or to a nonmetallic box with integral means for grounding devices.

(2)An equipment grounding conductor or equipment bonding jumper is connected to an equipment grounding termination of the snap switch.

Exception to (B): Where no grounding means exists within the snap-switch enclosure or where the wiring method does not include or provide an equipment ground, a snap switch without a grounding connection shall be permitted for replacement purposes only. A snap switch wired under the provisions of this exception and located within reach of earth, grade conducting floors, or other conducting surfaces shall be provided with a faceplate of nonconducting, noncombustible material.


[This message has been edited by iwire (edited 10-08-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals