The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (DanK, LongRunner), 228 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95813 - 10/07/05 10:51 AM Actuators for dampers
bdh45 Offline
Junior Member

Registered: 07/21/05
Posts: 2
Are HVAC actuators for commerecial dampers considered motors? Do they have to meet the disconnect requirement in NEC 430.101? Any opinions would be appreciated.

Top
2014 / 2011 NEC & Related Books and Study Guides
#95814 - 10/07/05 01:16 PM Re: Actuators for dampers
raider1 Offline
Member

Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
I would tend to classify a damper actuator as an appliance.

422.31 (A): For permanently connected appliances rated at not over 300 VA or 1/8 HP, the branch-circuit overcurrent device shall be permitted to serve as the disconnecting means.

Most of the damper actuators that I have seen are pretty small.

Just MHO.

Chris

Top
#95815 - 10/08/05 12:11 AM Re: Actuators for dampers
Sparks30 Offline
Member

Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
Most of the actuators I work on are 24v class 2. No need for disco.

Top
#95816 - 10/08/05 05:46 AM Re: Actuators for dampers
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Most of the actuators I work on are 24v class 2. No need for disco.


I do not see the fact that it is class 2 as the determining factor.

Disconnect switches are not only to keep us from getting shocks but also to keep us from getting caught in moving parts.

Many 24 volt damper motors can provide enough torque to amputate a finger.

I would like to believe that raider1 has the answer with 422.31 (A) but I am really not sure.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top