#95742 - 10/03/05 02:01 PM 310.4
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
A building has an existing 400 amp service with a 3" rigid riser existing.

They make the service 800 amp and add another 3-1/2" riser with the same conductor type, size, insulation, length, and terminated in the same manner.

Would this be a violation?

Does the raceway having the same physical charactristics include the size of the conduit?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95743 - 10/03/05 02:11 PM Re: 310.4
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Red tag from me
_________________________
Ryan Jackson,
Salt Lake City
Top
#95744 - 10/03/05 02:46 PM Re: 310.4
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Ryan--Would you mind elaborating a little. Just curious about the interpretation.

Thanks
Top
#95745 - 10/03/05 03:16 PM Re: 310.4
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
SteveT, I'm curious how you turn a 400-amp service into an 800-amp service without replacing the gear. It sounds like you're describing some kind of add-on.

Dave
Top
#95746 - 10/03/05 03:20 PM Re: 310.4
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
Quote:
310.4 Where run in seperate raceways or cables, the raceways or cables shall have the same physical characteristics.


3" and 3 1/2" seem to be different physical characteristics to me.
Top
#95747 - 10/03/05 03:25 PM Re: 310.4
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Steve I imagine Ryan is thinking of this part of 310.4

Quote:
Where run in separate raceways or cables, the raceways or cables shall have the same physical characteristics.


Tiger one quick and easy way is to provide 800 amp metering and add a second 400 amp service disconnect switch next to the original.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95748 - 10/03/05 03:25 PM Re: 310.4
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
They are replacing the gear.

I was just thinking the different physical characteristics tended more towards meaning the same type of metal, or not one metal and one PVC.

Does anyone have a reason why this would or could be unsafe? (Assume the raceways are properly bonded and such)
Top
#95749 - 10/03/05 03:28 PM Re: 310.4
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
I personally don't think there would ever be an issue with this install. But you are trying to avoid any differences between the paths. If you have a smaller pipe you would have a change in heat disipation and inductance for example, which might result in one path taking a larger amount of current.
Top
#95750 - 10/03/05 03:42 PM Re: 310.4
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Size is definitely a physical characteristic of a raceway.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95751 - 10/03/05 06:13 PM Re: 310.4
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I thinbk that cite came from a discussion of "parallel" feeders. What I see, instead, are two separate service drops, going to two separate disconnects.

If these are then combined at a panel, I see all sorts of "multiple feed" issues."

If they are segregated from each other, all the way to the outlets, then we have two separate services on one building.

As I understand parallel feeds, they have to start, and end, at the same places.....not a separate disconnects.
If that is the case, I would have preferred a larger riser, with larger wires, coming from a single disconnect to a single weatherhead. Then, if the PoCo wanted to run a parallel feed, they would join at the weatherhead.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals