The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (geoff in UK), 338 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95717 - 09/29/05 04:27 PM disconnecting means from building
gserve Offline

Registered: 03/11/03
Posts: 92
Is there a requirement in the code like in article 550 that addresses a maximum distance from the building to have a disconnect? I would like to have a pole mounted service and then feed the building which is 200' away there will be a main breaker in the panel closet to the point of entrance inside the building. Basically service on pole and feeder to building, service at building treated as sub-panel with isolated neutral,4 wire and also a GES. Or in other words how far can the service disconnecting means be from the building

2014 / 2011 NEC & Related Books and Study Guides
#95718 - 09/29/05 05:04 PM Re: disconnecting means from building
jw electric Offline

Registered: 09/08/05
Posts: 108
Loc: Asheboro, NC
Could this building fall under the scope of ARTICLE 547 Agricultural Buildings?

#95719 - 09/30/05 12:11 PM Re: disconnecting means from building
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
230.70(A)(1) requires the service disconnecting means to be either outside or inside the building nearest the point of entrance. And, 225.32 requires a disconnecting means for a remote building to be inside or outside, nearest the point of entrance of the conductors.
There are no numbers given, and it is up to the authority having jurisdiction to determine just how far away from the point of entrance constitutes "nearest".