#95651 - 09/25/05 08:26 PM splices
Tripp Offline
Member
Registered: 09/20/05
Posts: 99
Last week at work we had a problem where the carpenter installing medicine cabinets sent a screw through one of our NM cables and caused a short. My apprentice suggested that in lieu of tearing into a lot of sheetrock to re-run the swichtleg to the vanity light, we could just cut into the rock in the one spot where the screw hit, splice the romex there and be done. He said that there was a "UL-approved" splicing device, approved for in-the-wall splices, and that he had personally used one of these devices in the past.

My reading of NEC 300.15 would expressly forbid such a practice and I have never before heard of such an "approved" device. Anyone else?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95652 - 09/25/05 08:54 PM Re: splices
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
You are correct. He is not.
_________________________
Ron
Top
#95653 - 09/25/05 08:54 PM Re: splices
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
There has been talk of this on other posts (possibly I saw it at a different forum, I don't remember), I think the consensus was there is some device but it is not for conceiled work behind walls.
Top
#95654 - 09/25/05 08:55 PM Re: splices
DSpanoudakis Offline
Member
Registered: 08/31/05
Posts: 89
Loc: Astoria, Queens, N.Y.C.
He is the apprentice, you are not.
Top
#95655 - 09/25/05 08:58 PM Re: splices
jw electric Offline
Member
Registered: 09/08/05
Posts: 106
Loc: Asheboro, NC
Tyco Electronics makes a NM cable interconnection device that is designed to be concealed in the wall. Care needs to taken that there is no violation of the NEC.

For more information on these devices see the following sections of the 2005 NEC.
545.13, 550.15(K), 551.47(O), 552.48(N) and 690.32. These are the only places in the 2005 NEC that permits the interconnection device. For more information see UL file number E57250.
_________________________
Mike
Top
#95656 - 09/25/05 11:55 PM Re: splices
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I agree with Mike (JW) here, a few companies now make a listed in the wall splice for NM.

I suggest a look at 334.40(B)

You may not have been able to use these for the repair though.

Bob

[This message has been edited by iwire (edited 09-26-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95657 - 09/26/05 06:34 AM Re: splices
dlhoule Offline
Member
Registered: 04/28/05
Posts: 73
Loc: Saline, MI 48197
Iwire Just curious. Why would you want to fish a splice into a wall? 334.40B state you can do this during rewiring in existing buildings where the cable is concealed and fished.
Top
#95658 - 09/26/05 09:11 AM Re: splices
jw electric Offline
Member
Registered: 09/08/05
Posts: 106
Loc: Asheboro, NC
Quote:
I suggest a look at 334.40(B)


Thank you Bob I missed the most important one

_________________________
Mike
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals