#95632 - 09/22/05 04:43 PM Feeders and disconnect questions
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I have a job coming up in the next few weeks and I could really use some advice on what needs to be done up to code.

What I have is a separate building being fed from a multi-family dwelling. Two ungrounded conductors, and one grounded conductor (no ground), feeding a butcher block type business. The service to the building is under a 70 amp, 2-pole federal breaker at the main panel and #4 cu is being used.

At the point of attachment, the conductors are fed into a 1 - 1/4" RMC and LB'ed from there into the building. The panel is NOT at the nearest point of entrance and is at least 50' from the entrance point.

The work I'll be doing is re-attaching those service conductors to a new piece of RMC because the conductors are now secured by a vent stack. I know, lol, now I've seen it all.

My question is, since I'll be doing work to the service entrance, will I need to install a disconnect switch at the nearest point of entry inside the building? I've read the Code requirements in article 250.32 for the grounding update that I'll need to do. I just need to know if I NEED a new disconnect inside the building.

Thanks :-)
Top
2017 / 2014 NEC & Related Books and Study Guides
#95633 - 09/26/05 04:16 PM Re: Feeders and disconnect questions
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
The code reads inside or outside. Try to sell it to the owners but if they say no and the inspector calls you on it they will think you sand bagged them.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#95634 - 09/27/05 06:26 AM Re: Feeders and disconnect questions
jw electric Offline
Member
Registered: 09/08/05
Posts: 106
Loc: Asheboro, NC
Thhis sounds like feeders from the mulitfamily dwelling.
Will the conductors have an overcurrent device on it from the mulitfamily dwelling?

If it does then Part II of 225 will come into play. See 225.30 through 225.40.

If you have any questions we will discuss them.
_________________________
Mike
Top
#95635 - 09/27/05 06:40 PM Re: Feeders and disconnect questions
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Jw, yes, the feeders coming from the multi-family dwelling have OCP. They are protected by a 2P 70 amp Federal CKT BKR.


Thanks for the replies. It is sincerely appreciated. I'm just trying to be the best electrician I can be. I have read several sections of the NEC and have concluded that I should treat this job as I would any normal service, including a disconnect at the nearest point of entrance. I'm also going to drive 2 ground rods to provide a good path to ground because right now there is no EGC!

I guess my next question would be this, do I need to bond the EGC to the neutral conductor at the main disconnect? I'm thinking yes I should based on it being the service entrance point.

Thank you all.

--Ron

[This message has been edited by ShockMe77 (edited 09-27-2005).]

[This message has been edited by ShockMe77 (edited 09-27-2005).]
Top
#95636 - 09/27/05 06:56 PM Re: Feeders and disconnect questions
jw electric Offline
Member
Registered: 09/08/05
Posts: 106
Loc: Asheboro, NC
If you install two hots and a grounded (neutral) and no equipment grounding conductor and there is no metal paths (water, gas or other pipes) between the two buildings then treat it like a new service.

And if installing four conductors or a metal path is present then a sub panel.

Grounding electrode system is required
_________________________
Mike
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals