The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 327 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95629 - 09/22/05 12:06 PM Liquidtight Flex Metal Conduit
InspectorE Offline

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
Section 350.30(A), Exception 1 indicates that LFMC does not have to be secured within 12 inches of a box where it is fished. I generally take that to mean "old work". I am wiring a new home made with structural insulated panels (SIPs). There are wiring/plumbing chases precut into the foam core, making it possible to "fish" conduit through, but it would be very difficult to secure the conduit. Even though it is new, SIPs have the physical characteristics of old as you don't have access to the core. Do I have to secure the LFMC or is it considered to be "fished" even though it is new construction?

The Code doesn't seem to change quickly enough to deal with any new type of construction, so you have to make a judgement call.


2014 / 2011 NEC & Related Books and Study Guides
#95630 - 09/22/05 12:40 PM Re: Liquidtight Flex Metal Conduit
raider1 Offline

Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
I think you are reading to much into this.

The code says "Exception No. 2: Where LFMC is fished."

There are times on new construction that, because of an oversight or a change, that you may need to fish a conduit.

If it is fished it is fished regardless of if it is "old work" or a new ground up project.


#95631 - 09/22/05 03:37 PM Re: Liquidtight Flex Metal Conduit
HotLine1 Online   content


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
I concur with Raider1. Fishing does not require support.