The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Faricating Guards out if Lexan?
by frank
Today at 04:33 PM
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 9
frank 9
Who's Online
1 registered (LongRunner), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#95560 - 09/21/05 02:32 PM Reducing Washers
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Does anyone have any information on the use of reducing washers?
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#95561 - 09/21/05 02:37 PM Re: Reducing Washers
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
UL White Book

OUTLET BUSHINGS AND FITTINGS (QCRV)

 Quote:
GROUNDING
Metal reducing washers are considered suitable for grounding for use in
circuits over and under 250 V and where installed in accordance with
ANSI/NFPA 70, ‘‘National Electrical Code.’’


That's all I have except they make big holes small.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#95562 - 09/21/05 03:01 PM Re: Reducing Washers
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks Bob- That's what I needed.
_________________________
George Little

Top
#95563 - 09/22/05 04:29 AM Re: Reducing Washers
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
That information really makes me question the technical expertise of UL.
Don
_________________________
Don(resqcapt19)

Top
#95564 - 09/22/05 06:09 AM Re: Reducing Washers
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Don I think the problem is the difference between test conditions and real life.

I have no doubt you or I could make reducing washers carry fault current if we used a wire brush to remove all paint from the enclosure and tightened the lock nuts decently.

However I know I see reducing washers all the time that are up against paint and loose.

I think an inspector could cite 250.12 Clean Surfaces almost every time.

Personally I dislike everything about reducing washers.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#95565 - 09/22/05 06:30 AM Re: Reducing Washers
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I discussed this matter with the UL representative of CMP 5 (Article 250). He was surprised as well, but looking at the listing standard, it appears as though under test conditions reducing washers that are listed are capable of carrying a tremendous amount of fault current. I don't recall the exat test now, but it was several thousand amps for a substantial duration.
_________________________
Ryan Jackson,
Salt Lake City

Top
#95566 - 09/22/05 08:45 AM Re: Reducing Washers
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
I'm sorry, but if the test conditions do not represent a real world installation, the results are worthless.
Don
_________________________
Don(resqcapt19)

Top
#95567 - 09/22/05 11:22 AM Re: Reducing Washers
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
I vote with Bob. Reducing washers keep the connector from falling out but I would use a bonding nut if I wanted to make a secure grounding connection.
_________________________
Greg Fretwell

Top
#95568 - 09/22/05 04:27 PM Re: Reducing Washers
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Reducers -- gotta hate 'em....

Every time I see them it's a hack job.

I particularly dislike reducers used at NEMA3R disconnects where the installer is shrinking back from a 1 inch KO goof.
_________________________
Tesla

Top
#95569 - 09/22/05 05:48 PM Re: Reducing Washers
livetoride Offline
Member

Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
I hate RE plates. I would rather screw a plate in the can and make sure there is a ground wire. I have had inspectors fail an installation; he wanted reducing washers; I had bolted a cover plate to the top of the box and had a grounding bushing and ground wire in the EMT. My way was better and I proved it to him with a megger. He made me change it to pass inspection. Still scratching my head Rod.