#95533 09/19/05 12:30 AM
Joined: Sep 2005
Posts: 8
C
cruzer Offline OP
Junior Member
do you have to pull a ground to the transformer when the last ten feet is pvc.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#95534 09/19/05 02:09 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Yep, even when not in PVC...

See 250.20 to determine if it needs to grounded (odds are it does) and 250.30 if deemed seperately derived system.


Mark Heller