#95495 - 09/16/05 06:45 PM EGC for 4 subpanels.
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
I finished a fourplex four meter pack with four disconnects on one enclosure.And i have four 60Amp feed through one conduit to each subpanel that are installed side by side in a 36"x48" enclosure. I have pulled only one #10 EGC that is being daisy chained from one panel to the next.
I have a feeling that i need four #10EGC.
Am I correct?

Please show NEC reference because i can not find it.

Thank you
Edward
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#95496 - 09/16/05 07:28 PM Re: EGC for 4 subpanels.
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
And i have four 60Amp feed through one conduit to each subpanel that are installed side by side in a 36"x48"

what kind of raceway?

h20
Top
#95497 - 09/16/05 07:59 PM Re: EGC for 4 subpanels.
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
One EMT conduit with four "C" conduilets that feed each panel separately. It is not a through feed installation.
I will try to submit picture.

Thanks
Edward
_________________________
Thanks
Edward
Top
#95498 - 09/16/05 08:07 PM Re: EGC for 4 subpanels.
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Ed, the EMT itself should qualify as the EGC for each panel. Otherwise, yes, each feeder should have its own EGC, I believe.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#95499 - 09/17/05 03:47 AM Re: EGC for 4 subpanels.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
One EGC for all the circuits is OK.

Quote:
250.122(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.


Not sure the power company will be happy with the feeders from 4 different meters to all be in the same conduit.



[This message has been edited by iwire (edited 09-17-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95500 - 09/17/05 04:33 AM Re: EGC for 4 subpanels.
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
I don't know why the power company would care, since the feeders are all downstream of the main OCP. The AHJ might care, but I don't see any real issues with it.
Top
#95501 - 09/17/05 04:43 AM Re: EGC for 4 subpanels.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Power theft would be the power company's issue.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95502 - 09/17/05 09:28 AM Re: EGC for 4 subpanels.
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I think 250.24(C) is the section we want.

As I read it, you are only required to have on GEC (wire to a ground rod). The utility neutral, however, must be bonded to the case of each of the disconects- so the egc will terminate to the neutral buss at each disconnect as well.
Top
#95503 - 09/17/05 09:33 AM Re: EGC for 4 subpanels.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Reno I believe the GEC would be at the meter stacks with the service disconnect(s) the wires in the EMT are feeders not service conductors.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#95504 - 09/17/05 04:12 PM Re: EGC for 4 subpanels.
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I agree, Iwire.....I only brought up the GEC as this is the sort of application where things get confused easily. After all, there is the question of what to do with the EGC once it reaches the panel.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals