The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95454 - 09/13/05 10:42 PM bushing
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
where in nec does it say you have use a pvc connector at the end of a pipe in the ground fed with uf?

is this a wives tale. 300.4 apply?
and the wire is smaller then #4 so the only bushing requirement doesnt apply.

i always do it(trained this way) but wonder if i have to.

h20

Top
2014 / 2011 NEC & Related Books and Study Guides
#95455 - 09/14/05 02:09 AM Re: bushing
jw electric Offline
Member

Registered: 09/08/05
Posts: 108
Loc: Asheboro, NC
How about 300.5 (H) Bushing. A bushing, or terminal fitting, with an integral bushed opening shall be used at the end of a conduit or other raceway that terminates underground where the conductors or cables emerge as a direct burial wiring method. A seal incorporating the physical protection characteristics of a bushing shall be permitted to be used in lieu of a bushing.

Could this be it?
_________________________
Mike

Top
#95456 - 09/14/05 12:36 PM Re: bushing
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
this 300.5 must be it....
thanks

h20

Top
#95457 - 09/14/05 01:37 PM Re: bushing
eprice Offline
Member

Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
Also 300.15(C)

Top