#95340 - 09/07/05 06:51 PM LV Lighting Cable woes
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
We know that LV cales can't pass through or be concealed in walls per Article 411.
The aggravation that some of these installations pose, along with trying to explain to homeowners why you can't use LV cable, makes me wonder why someone doesn't get a UL listing for a LV cable that can be concealed.
It would eliminate the "junction/transition" fittings, and probably make the job go much smoother.


Any thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95341 - 09/07/05 07:56 PM Re: LV Lighting Cable woes
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Quote:
...makes me wonder why someone doesn't get a UL listing for a LV cable that can be concealed.


Isn't that called, "Romex"?
Top
#95342 - 09/08/05 03:56 AM Re: LV Lighting Cable woes
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Romex, indeed.

However, depending on the installation conditions, accomodating the transition back to LV isn't always that easy. Even with the devices designed to do so.
Top
#95343 - 09/08/05 07:02 PM Re: LV Lighting Cable woes
Jim M Offline
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Redsy,

LV cable will be allowed in walls in the 05 Code. One AHJ will let me sleeve LV thru ent in the walls.

I think there are some conditions but my notes are not with me.
Top
#95344 - 09/09/05 12:27 AM Re: LV Lighting Cable woes
e57 Offline
Member
Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Attention should also be paid to the listing of the fixture as well, some dont allow modification to the wiring and terminations.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#95345 - 09/10/05 03:23 PM Re: LV Lighting Cable woes
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
The 2005 code will allow cables feeding low voltage lights to be concealed if the power supply is a listed class 2 power supply and the cable is also listed as a class 2 cable. Due to the power source limitations (see table 11(A) in Chapter 9), this may not be practical for some installations.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals