We know that LV cales can't pass through or be concealed in walls per Article 411.
The aggravation that some of these installations pose, along with trying to explain to homeowners why you can't use LV cable, makes me wonder why someone doesn't get a UL listing for a LV cable that can be concealed.
It would eliminate the "junction/transition" fittings, and probably make the job go much smoother.


Any thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#95341 - 09/07/05 07:56 PM Re: LV Lighting Cable woes
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
Quote:
...makes me wonder why someone doesn't get a UL listing for a LV cable that can be concealed.


Isn't that called, "Romex"?
Top
#95342 - 09/08/05 03:56 AM Re: LV Lighting Cable woes
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Romex, indeed.

However, depending on the installation conditions, accomodating the transition back to LV isn't always that easy. Even with the devices designed to do so.
Top
#95343 - 09/08/05 07:02 PM Re: LV Lighting Cable woes
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
Redsy,

LV cable will be allowed in walls in the 05 Code. One AHJ will let me sleeve LV thru ent in the walls.

I think there are some conditions but my notes are not with me.
Top
#95344 - 09/09/05 12:27 AM Re: LV Lighting Cable woes
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Attention should also be paid to the listing of the fixture as well, some dont allow modification to the wiring and terminations.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#95345 - 09/10/05 03:23 PM Re: LV Lighting Cable woes
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
The 2005 code will allow cables feeding low voltage lights to be concealed if the power supply is a listed class 2 power supply and the cable is also listed as a class 2 cable. Due to the power source limitations (see table 11(A) in Chapter 9), this may not be practical for some installations.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals