The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#95317 - 09/07/05 05:00 PM 310 15 (B)
big guy Offline

Registered: 12/19/03
Posts: 52
Loc: pa
Am I right in saying if you read 310 15 (B) (4)
A neutral does not have to be derated if it is only serving to carry the laod form one ungrounded conductor.
For Ex

You have 9 # 10 in A 3/4 pipe
4 hot wires
4 neutral wires
1 ground
There would be 4 current carrying conductors in this pipe. The load would be only be recp.

Is this right thanks

2014 / 2011 NEC & Related Books and Study Guides
#95318 - 09/07/05 05:42 PM Re: 310 15 (B)
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
Ah, we have to know what the loads are???

Incandescent lighting, fluorescent lighting, motors, etc.


#95319 - 09/07/05 05:46 PM Re: 310 15 (B)
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Big Guy, in a two wire circuit, both conductors are current carrying, there is no neutral.

Now if the grounded conductor is shared between legs it becomes a neutral.


#95320 - 09/08/05 02:51 AM Re: 310 15 (B)
big guy Offline

Registered: 12/19/03
Posts: 52
Loc: pa
The load is just common 120 volt recp.

I want to know if the neutral is a current carrying conductor

If each hot wire has is own neutral.Do you have derate the neutral with the hot wires.
I hope this clears it up better.


#95321 - 09/08/05 03:03 AM Re: 310 15 (B)
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Big Guy, yes in your two wire circuits both wires are current carrying conductors, it wouldn't matter what the voltage is, see the first graphic.

In your question you have 8 current carrying conductors.


#95322 - 09/08/05 03:06 AM Re: 310 15 (B)
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The short answer is yes the white wire in these circuits is a current carrying conductor.

You do not have a 'neutral' in that circuit. Look at Rogers upper diagram.

What you have you have in the language of the NEC an ungrounded and a grounded conductor.

Your 3/4" pipe has 8 current carrying conductors for the purposes of derating.
Bob Badger
Construction & Maintenance Electrician

#95323 - 09/08/05 03:08 AM Re: 310 15 (B)
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Yes and yes.

Look at the diagrams that Roger posted. Any current flowing in a hot wire has to be balanced somewhere. If each hot wire has its own separate neutral, then the current flowing in that neutral _must_ be equal to the current flowing in the hot. Therefore if the hot is counted as a current carrying conductor, the neutral must also be counted.

_Shared_ neutrals under _some_ conditions need no be counted as current carrying conductors. This is because the current flow in the hot will be balanced by the current flow in the opposite hot.

Remember: the current flow in a string of series connected elements is always the same everywhere.

In your example, there would be 8 current carrying conductors.


#95324 - 09/15/05 04:58 PM Re: 310 15 (B)
ShockMe77 Offline

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
This thread is why I think this forum is good.

Thanks guys!

#95325 - 09/17/05 11:41 PM Re: 310 15 (B)
Local Offline

Registered: 07/25/04
Posts: 19
Loc: Sacramento
While I agree with the ideas posted so far I think the NEC says you do not need to count the grounded conductor as a current carrying conductor for the purpose of derating in this instance. The text of the code reads:

310.15 (B)(4)(a)
A Neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(2)(a)

I interpret this to read:
"One hot and one neutral count as 1 CCC when applying 310.15(B)(2)(a)"

A multi-wire circuit would require counting the grounded conductor according to 310.15(B)(4)(b&c)

Have I missed the boat? What do you guys think?

[This message has been edited by Local (edited 09-18-2005).]

#95326 - 09/18/05 12:47 AM Re: 310 15 (B)
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Local it is talking about at least a 3-wire ciruit. "...unbalanced current from other conductors of the same circuit"

But I think there's something wrong with the wording here. I think it should be balanced current! Otherwise it is a current carrying conductor, right? At least in single phase it would be. Hmmmm. It's late, and I need beer.
Mark Heller
"Well - I oughta....." -Jackie Gleason

Page 1 of 2 1 2 >

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals