The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95279 - 09/06/05 04:00 PM Overload?
jes Offline
Member

Registered: 07/12/02
Posts: 103
Loc: CT
15 Amp, 125 volt branch circuit with duplex 15 Amp, 125 volt receptacles. Plugged into a single duplex are two 6.5 Amp (nameplate) commercial referigerators, one into each position. For the sake of discussion there are no other loads. Does this violate ANY ratings or NEC requirements?

Top
2014 / 2011 NEC & Related Books and Study Guides
#95280 - 09/06/05 04:14 PM Re: Overload?
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
I would say no.
I believe a refrigerator is not a continuous load ( on for 3 or more hours). The compressor will cycle on and off but should not run continuous.

Top
#95281 - 09/06/05 05:27 PM Re: Overload?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
210.21(B)(2)
If the "duplex" receptacle is considered 2 receptacles, (and I believe it is) you would have a violation.

Top
#95282 - 09/06/05 05:42 PM Re: Overload?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Redsy, since this is in fact two receptacles, neither one would be loaded to the maximum limit of Table 210.21(B)(2) for a 15 amp receptacle.

Roger

Top
#95283 - 09/06/05 06:24 PM Re: Overload?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
OK, so it's per each receptacle?

Top
#95284 - 09/06/05 07:40 PM Re: Overload?
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
No overload, no violation but poor design. Just a matter of time before both units start at the same time and that could spell problem.
_________________________
George Little

Top
#95285 - 09/08/05 02:27 AM Re: Overload?
jes Offline
Member

Registered: 07/12/02
Posts: 103
Loc: CT
And no argument...

To change the question slightly...
Suppose the duplex were split and each receptacle had it's own 15 Amp circuit.
A load of 12 Amps could be connected to each, giving a total current of 24 amps through a standard, everyday, less than $1, duplex receptacle, correct?

Top
#95286 - 09/08/05 03:50 AM Re: Overload?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Yes that is correct.

Now how long would that cheap receptacle would last is another question altogether.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top