#95273 - 09/06/05 03:29 PM GFCI Near Laundry Sink?
BigJohn Offline
Member
Registered: 03/06/04
Posts: 391
Loc: Boston, MA
Recently red-tagged on a new-house construction because there was no GFCI protection for a receptacle on the wall opposite of a laundry-room sink. Inspector said all receptacles within 6' of the sink in any direction must have ground fault protection.

Not saying it isn't a good idea, but I couldn't find the article requiring it. 2002 NEC. Anyone have a reference?

-John
Top
2017 / 2014 NEC & Related Books and Study Guides
#95274 - 09/06/05 03:48 PM Re: GFCI Near Laundry Sink?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
BigJohn, it is a new wording in 210.8(A)(7) of the 05 NEC.


Quote:
Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink


If you are still under 02 the inspector is wrong.

Roger
Top
#95275 - 09/06/05 03:49 PM Re: GFCI Near Laundry Sink?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
210.8 (a) (7) of 2005 NEC

John
_________________________
John
Top
#95276 - 09/06/05 03:52 PM Re: GFCI Near Laundry Sink?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
I snuck that one in on you John.

Roger
Top
#95277 - 09/06/05 03:56 PM Re: GFCI Near Laundry Sink?
BigJohn Offline
Member
Registered: 03/06/04
Posts: 391
Loc: Boston, MA
I knew it. And I had to drive thirty miles to correct that bogus violation.

Thanks, gentlemen.

-John
Top
#95278 - 09/07/05 03:26 PM Re: GFCI Near Laundry Sink?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Roger:
OK, you type faster than me. I was going back to edit, but ya got me.

John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals