The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#95157 - 09/01/05 01:18 PM Fusing Circuits
kyelectric Offline

Registered: 08/30/05
Posts: 64
Recently we installed a new circuit that shares a 60 amp disconnect with another circuit. Right now the 60 amp disconnect has 30 amp fuses. The wire size going to the other ciruit is #10. My new circuit is going to a jib crane with a FLA of 1 Amp. I ran #12 wire and installed 1 8/10 fuses on a secondary disconnect that is closer to the jib crane. I would like some input as to whether the #12's I ran are safe with the main disconnect having 30 amp fuses since my new disconnect for the circuit I installed has 1 8/10's fuses installed downstream? Thanks for the great input on my last question and any help on this one would be appreciated as well.

2014 / 2011 NEC & Related Books and Study Guides
#95158 - 09/02/05 07:12 AM Re: Fusing Circuits
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Tap rules must be followed when overcurrent protection is not provided at the "start" of a circuit, 240.21.

Does your installation meet all requirements of any part of 240.21(B), specifically look at (2).