#95157 - 09/01/05 01:18 PM Fusing Circuits
kyelectric Offline
Member
Registered: 08/30/05
Posts: 64
Recently we installed a new circuit that shares a 60 amp disconnect with another circuit. Right now the 60 amp disconnect has 30 amp fuses. The wire size going to the other ciruit is #10. My new circuit is going to a jib crane with a FLA of 1 Amp. I ran #12 wire and installed 1 8/10 fuses on a secondary disconnect that is closer to the jib crane. I would like some input as to whether the #12's I ran are safe with the main disconnect having 30 amp fuses since my new disconnect for the circuit I installed has 1 8/10's fuses installed downstream? Thanks for the great input on my last question and any help on this one would be appreciated as well.
Top
2017 / 2014 NEC & Related Books and Study Guides
#95158 - 09/02/05 07:12 AM Re: Fusing Circuits
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Tap rules must be followed when overcurrent protection is not provided at the "start" of a circuit, 240.21.

Does your installation meet all requirements of any part of 240.21(B), specifically look at (2).
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals