#95137 - 08/31/05 10:06 PM EMT Support
jtedson Offline
Junior Member
Registered: 05/10/04
Posts: 1
Loc: Federal Way,WA,USA
There is a little debate at work about the wording of the code on this issue. In 358.30(A) it says "other tubing terminations" shall be securly fastened within 3 ft. One of my fellow workers insists this means every coupling. While most of agree this is good practice to secure the pipe close to a coupling if practical, we feel the code is referring to a connector in this instance. Any feedback on this would be great. Thank you in advance.
Top
2017 / 2014 NEC & Related Books and Study Guides
#95138 - 08/31/05 10:30 PM Re: EMT Support
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
358.30(A) securely fastened. emt shall be securely fastened in place at least every 3 m (10 ft.) in assition, each emt run between termination points shall be securely fastened within 900 mm (3 ft.) of each outlet box, junction, box, device box, cabinet, conduit body, or other tubing termination.

ok i think they are reading to hard into "other" forgetting the word "termination" within 3 ft of termination and certainly couplings are not terminating but merely continuing until one does terminate.

imho

h20
Top
#95139 - 09/01/05 03:14 AM Re: EMT Support
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
I agree with h20, a coupling is not a termination.

If couplings were to be included, the word "coupling" could have been in the article.

Check the link below for anothers opinion.
http://www.mikeholt.com/reprint_request.php?url=http://www.mikeholt.com/graphics/348-13.gif

Roger
Top
#95140 - 09/03/05 04:53 AM Re: EMT Support
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I had this same misconception and it stems from the fact the code was changed.

The section used to actually say "fitting" a coupling is definitely a fitting.

1990 NEC
Quote:
348-12 Supports. Electrical metallic tubing shall be installed as a complete system as provided in Article 300 and shall be securely fastened in place at least every 10 feet (3.05m) and within feet (914mm) of each outlet box, junction box, cabinet or fitting.


This may or not be the same wording in the 1993 NEC I do not have a 1993 NEC available.

Personally I find the change to be in the wrong direction, IMO a support should be required within 3' of a EMT coupling.



[This message has been edited by iwire (edited 09-03-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals