#94954 - 08/19/05 02:02 PM Disconnect
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I was doing a 3-phase 277/480 ahu unit today, then the hvac guy tells me he needs a 110v outlet for his condensate pump. I tell the boss this he say come off the the 110 panel join the 277 pipe together to the disco then feed threw the disco for the 110.
I know no feed through for panel, how about disco?
Top
2017 / 2014 NEC & Related Books and Study Guides
#94955 - 08/19/05 02:10 PM Re: Disconnect
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You end up back at 312.8 and you have to ask yourself IS "adequate space for this purpose is provided.".
I would bet a couple of 12 or 14 guage wires are not going to put this cabinet over 40% of the available wiring space. (or 75% of the cross section where the wires run)
_________________________
Greg Fretwell
Top
#94956 - 08/19/05 03:57 PM Re: Disconnect
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Panel or Disconnect either can be 'run through' as long as there is enough space.

It would be darn near imposable to overfill a panel with branch circuit wiring.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#94957 - 08/19/05 04:51 PM Re: Disconnect
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
quote"It would be darn near imposable to overfill a panel with branch circuit wiring."

Boy in the 60's they sure knew how to do it. I go to a lot of jobs with old GE load centers so packed up with wire the cover almost springs off when the screws are loosened. Of course the # of wires is still comparable to modern stuff, it's just the boxes were so little, and the long spare length's left on the wires before terminating at the breakers makes for a big crowd.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals