ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#94824 - 08/15/05 01:27 PM Trade Name/Connector
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
When running a GEC from either a SDS or a panel, the GEC must be protected from damage, is this correct?

Have found alot that are either tywrapped up, or even leave the MDP via a romex connector and go through a sheetrocked wall and then over to building steel.
Most of it exposed..

I remmember seing somewhere on one of these threads a connector that was used on EMT that housed the GEC. This connector bonded the EMT,or Rigid at the top where the GEC left the pipe.

Does this type connector have a trade name?

Any help here?

And another question, do most of you bond the SDS in the transformer or at the service panel?

Which is best and why?


Dnk.......
Top
2017 / 2014 NEC & Related Books and Study Guides
#94825 - 08/15/05 01:52 PM Re: Trade Name/Connector
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Dnk, Click here for the thread on "City Hubs"

Check out 250.64, the GEC doesn't necessarily need protection.

Roger
Top
#94826 - 08/15/05 03:25 PM Re: Trade Name/Connector
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Thanks for the link Roger.

I couldn't find where it stated they need protection, but remmembered that thread, and always wondered why you put them in pipe, with this "city hub".

Any explanation?
Is it just for asetics?(spelling)


Dnk........
Top
#94827 - 08/15/05 03:47 PM Re: Trade Name/Connector
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
250.64(E) requires the GEC to be bonded to any metal enclosure it passes through.

Without bonding the GEC, the current flow during a fault will be reduced, actually impeded.

Others may be able to explain it correctly.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#94828 - 08/15/05 04:52 PM Re: Trade Name/Connector
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Bob, I understood the bonding of the pipe, the arcing that would develope from the GEC to the pipe during a fault condition.

I even understand the reasoning of bonding both ends of the pipe to the GEC and the enclosure,
But why in that thread, if the GEC doesn't have to be in pipe, do you put it in there?


Dnk.....
Top
#94829 - 08/15/05 05:39 PM Re: Trade Name/Connector
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Dnk, the reason we would do it if it's not needed for protection would be the engineering specifications require it.

Roger
Top
#94830 - 08/15/05 05:45 PM Re: Trade Name/Connector
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Roger, how would putting it in pipe help with spec's. Does it decrease overall impedance of the length of wire when done in pipe and properly bonded, or is this just something you normally see in hospitals and sensitive electronics labs.

I've never seen it done in my day like that in all the machine shops and commercial buildings I've seen.

But if it helps in overall performance, it is something I'd like to rethink and do.

Any more info you have on this application is appreciated.


Dnk.....
Top
#94831 - 08/15/05 06:11 PM Re: Trade Name/Connector
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Dnk, specs are not always for performance, alot of the times I see this in specs, it is basically for neatness or asthetics.

Now as far as performance is concerned, let's take the "Choke Effect" out of the conversation, and think parallel conductor.

When the metallic raceway and GEC are bonded together at both ends they become a parallel conductor reducing the resistance and impedance of the path, so with this in mind, it would make sense to bond the raceway and conductor regardless of any other considerations.

Roger
Top
#94832 - 08/15/05 06:36 PM Re: Trade Name/Connector
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
I always thought they were called "City clamps" (AKA ground hub) because for the longest time they were only required in the city I live in, I guess other cities want them too....

Is there a "country/rural/suburban clamp"?



[This message has been edited by e57 (edited 08-15-2005).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#94833 - 08/15/05 06:43 PM Re: Trade Name/Connector
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
DNK, what you are asking is answered "4 ga or larger does not *normally* require physical protection".
250.64(B) ...A 4 AWG copper or aluminum or larger conductor shall be protected if exposed to severe physical damage.

What is "severe"? Ask your AJH what it is that day.
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals