The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94760 - 08/12/05 03:18 PM NM-B in Crawl Spaces
BigJohn Offline
Member

Registered: 03/06/04
Posts: 352
Loc: Boston, MA
Does the NEC allow Romex to be run across the bottoms of floor joists in crawl spaces?

This is something I see done all the time, and I thought it was legit because of the accessibility of these places, and I see it pass on inspected new construction. But I can't find any article allowing it or exempting crawlspaces from 300.4.

Maybe everyone (rightfully) assumes that no inspector in their right mind is going into that crawl space to enforce this...?

-John

[This message has been edited by BigJohn (edited 08-12-2005).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#94761 - 08/12/05 04:02 PM Re: NM-B in Crawl Spaces
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I suspect they will cite;
334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface. The cable shall closely follow the surface of the building finish or of running boards.

... if anyone is willing to crawl in there for a peek.
_________________________
Greg Fretwell

Top
#94762 - 08/13/05 05:33 AM Re: NM-B in Crawl Spaces
macmikeman Offline
Member

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
It's not allowed where I'm at, unless # 6 guage or larger cable. I allways run along the face of the joists and drill thru cross blocking. Usually there is a beam holding up them joist and I staple to the face of that for perpendicular to the joist runs.

Top