i want to know if anybody can help me calculate if i can put a 1/2 HP disposer motor and a dishwasher that draws a nameplate or 9.1 amps on a 20 amp circuit.
Top
2017 / 2014 NEC & Related Books and Study Guides
#94720 - 07/06/05 09:39 AM Re: disposer/dish circuit
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Nominal FLA on a 1/2 HP motor is 9.8a (plus 25%) added to 9.1a seems to be too much for a multiple motor load.
If you are cord and plug connected they each do represent less than 50% of circuit ampacity so it might be "hold your nose" legal. I have seen this go both ways but the preferable solution is a multiwire circuit with 2 phases feeding the duplex.
_________________________
Greg Fretwell
Top
#94721 - 07/06/05 11:12 PM Re: disposer/dish circuit
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
thanks gf i just wondered if possible...
could you elaborate on the 50% since cord connected dishwashers are feasible and do provide disconnecting means for motor.

h2o
Top
#94722 - 07/07/05 09:39 AM Re: disposer/dish circuit
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
It all gets down to how you read
210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

Most inspectors would say all fixed in place equipment must be less than 50% but I have seen this stretched to say any one piece can't exceed 50%, particularly on an intermittant load like a disposal.
Vote me for "all".
_________________________
Greg Fretwell
Top
#94723 - 07/07/05 07:03 PM Re: disposer/dish circuit
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
One caution here....look at the FLA on the disposal, and not the "horsepower" rating. I have seen a lot of inflated "horsepower ratings" over the years.
Top
#94724 - 07/12/05 06:46 PM Re: disposer/dish circuit
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
"...lighting units (or) cord-and-plug-connected utilization equipment not fastened in place..."

Neither describe either a dishwasher or a disposer, so 210.23(A)(2) doesn't apply.

I routinely place both of these on a 20-amp circuit. A disposer is probably the epitome of an intermittent load.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#94725 - 07/12/05 06:55 PM Re: disposer/dish circuit
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
According to Insinkerator specs, the 1/2HP Badger 5 has an average current draw of 6.9A.
http://www.insinkerator.com/pdf/badger5.PDF
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#94726 - 08/10/05 06:27 AM Re: disposer/dish circuit
dlhoule Offline
Member
Registered: 04/28/05
Posts: 71
Loc: Saline, MI 48197
Good subject. I have been told that they make a 3 way switch that can be used in these applications. One position for dishwasher and other for disposal. Now having said that I personally have not seen one. Do they make them?
Top
#94727 - 08/10/05 07:23 AM Re: disposer/dish circuit
BobH Offline
Member
Registered: 10/16/04
Posts: 134
Loc: Newfane, N.Y USA
Any 3-way rated for the load would work.
Top
#94728 - 08/10/05 02:43 PM Re: disposer/dish circuit
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I am moving this to the NEC section.
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals