The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94711 - 08/10/05 03:33 AM Mixing DC with AC conductors?
MikeW Offline
Member

Registered: 06/03/02
Posts: 39
Loc: Michigan
Does the NEC allow 24vdc wires to be run in the same conduit with 120vac conductors?

What code section(s)?

thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#94712 - 08/10/05 04:21 AM Re: Mixing DC with AC conductors?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Mike,
Look at 300.3(C)(1), but make sure that you read the FPN that follows that section.
Don
_________________________
Don(resqcapt19)

Top
#94713 - 08/10/05 09:44 AM Re: Mixing DC with AC conductors?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Just remember that when you mix voltages in an enclosure or raceway you lose any latitide you might have had for "low voltage" in art 725. Everything is now treated like line voltage.
_________________________
Greg Fretwell

Top
#94714 - 08/13/05 05:17 AM Re: Mixing DC with AC conductors?
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
300.3 contains a similar requirement for this situation to one we have here -- That all conductors must be insulated for the highest voltage present.,

Top
#94715 - 08/13/05 06:28 PM Re: Mixing DC with AC conductors?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Paul,
You have to read and apply the FNP that follows the section that you have cited. The section doesn't really mean what it says.
Don
_________________________
Don(resqcapt19)

Top
#94716 - 08/14/05 05:12 AM Re: Mixing DC with AC conductors?
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Oh boy, I hadn't even started to read 725 before now. The definitions for class 2 and 3 circuits seem overly complex. This section is going to take some studying.

Top
#94717 - 08/14/05 05:43 AM Re: Mixing DC with AC conductors?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Paul,

 Quote:
The definitions for class 2 and 3 circuits seem overly complex. This section is going to take some studying


I wish you well, you must be a gluten for punishment if you want to try to make heads or tails of 725.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#94718 - 08/14/05 02:29 PM Re: Mixing DC with AC conductors?
Rhino Offline
Member

Registered: 06/28/04
Posts: 24
Loc: San Diego,California,USA
I wonder wether there are some practical issues at play as well.Such as some current being imposed (through induction)on the DC circuit causing havoc with the circuits on the DC power run.
To be safe i would go with the rule of thumb of not combining one with the other.
Along the lines of even if it is permissable -should it really be done??