The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 256 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#94700 - 08/09/05 09:24 AM Inside panels upside down...
foestauf Offline
Member

Registered: 08/01/05
Posts: 51
Loc: Florida
Here's the skinny. I'm doing simple track houses and I'm in an upstairs only unit, so the service wire comes from under the panel.
I decided that it looked too ugly to run the service into the panel then all the way around to teh lugs up top.
So I turned the panel upside down being that it is a Square D QO panel that has LINE written upside down and rightside up overtop the lugs.
Inspector says he doesn't like it, my supervisor has no problem with it...
Any possibility the inspector could push the issue?

Top
2014 / 2011 NEC & Related Books and Study Guides
#94701 - 08/09/05 09:52 AM Re: Inside panels upside down...
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I never underestimate what uninformed inspectors might "push" but what you are doing sounds perfectly legal.
Get the instructions from the panel and highlight the line where it says it can be mounted either way.
_________________________
Greg Fretwell

Top
#94702 - 08/09/05 02:17 PM Re: Inside panels upside down...
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
If it's MLO, I can't see any problem and I don't think there's any Code issues either.

Main Breaker? Again, I don't see a problem. I don't recall ever seeing a Code requirement that the Main breaker be on the top.

Anyone? Anyone? Bueller? Bueller?
_________________________
Stupid should be painful.

Top
#94703 - 08/09/05 03:10 PM Re: Inside panels upside down...
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
I always thought that circuit breakers that are mounted vertical, off must be downward
same as a disconnect.? Will have to research the big red book on this (05 nec)

Top
#94704 - 08/09/05 03:23 PM Re: Inside panels upside down...
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Go to this SQ D FAQ page and type in "upside down" in the search window.

Roger

Top
#94705 - 08/09/05 03:52 PM Re: Inside panels upside down...
Tiger Offline
Member

Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
It's not a violation. I also don't like it because the numbering stamped into the cover isn't reversable. I wish they made a door that was numbered for the upside down installation.

I install QO panels commercially from the bottom & running 3/0 around the inside of the panel to the top is no treat.

Dave

Top
#94706 - 08/09/05 03:58 PM Re: Inside panels upside down...
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
I install QO panels commercially from the bottom & running 3/0 around the inside of the panel to the top is no treat.


Buy commercial panels and you will not have that problem.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#94707 - 08/09/05 04:18 PM Re: Inside panels upside down...
Tiger Offline
Member

Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
Sorry, you lost me on that one, iwire. I'd consider a 200-amp, three-phase, main lug panel a commercial panel.

Dave

Top
#94708 - 08/09/05 04:31 PM Re: Inside panels upside down...
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Is it in a 14.5"W x 3.5"D cabinet or a 20"W x 6.5"D tub?

We only use the 14.5"W x 3.5"D cabinet panels once in a wile for temps.

The reason i brought it up was this statement.

 Quote:
I also don't like it because the numbering stamped into the cover isn't reversable. I wish they made a door that was numbered for the upside down installation.


I was just working on two Square D 100 amp MLO panels and they came with doors that hang right side up regardless of the interiors position and they come with stickers to number the dead front with so they are right side up.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#94709 - 08/09/05 04:35 PM Re: Inside panels upside down...
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Dave, actually a QO series is listed under SQ D's "Loadcenters" whereas say a NQOD would be listed under "Panelboards".

Generally speaking "Loadcenters" are more residential and / or lightweight in nature than a "Panelboard"


Roger

Top