The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#94649 - 08/04/05 05:19 AM Pool motor
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?

Top
2014 / 2011 NEC & Related Books and Study Guides
#94650 - 08/04/05 06:59 AM Re: Pool motor
Tiger Offline
Member

Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave

Top
#94651 - 08/04/05 11:41 AM Re: Pool motor
markp Offline
Member

Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).
_________________________
Mark
Kent, WA

Top
#94652 - 08/04/05 12:15 PM Re: Pool motor
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.
_________________________
Greg Fretwell

Top
#94653 - 08/04/05 12:37 PM Re: Pool motor
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.

Top
#94654 - 08/04/05 01:58 PM Re: Pool motor
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)
_________________________
Greg Fretwell

Top
#94655 - 08/04/05 02:25 PM Re: Pool motor
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....

Top
#94656 - 08/04/05 02:58 PM Re: Pool motor
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.
_________________________
Greg Fretwell

Top
#94657 - 08/04/05 03:11 PM Re: Pool motor
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......

Top
#94658 - 08/04/05 07:48 PM Re: Pool motor
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.