#94649 - 08/04/05 05:19 AM Pool motor
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Does the pool filter motor have to be on a dedicated feed?
Can you install the convience receptacle on the same feed as the pool motor?
Any thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#94650 - 08/04/05 06:59 AM Re: Pool motor
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
I don't find any requirement for the pool pump to be on a dedicated circuit without other outlets.

Dave
Top
#94651 - 08/04/05 11:41 AM Re: Pool motor
markp Offline
Member
Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
If the pool pump is hardwired, then this rule applies:

210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

So if you want receptacles on a hard wired motor circuit, then it can only draw half of the circuit's rating (which isn't likely with most 120V pool pumps).
_________________________
Mark
Kent, WA
Top
#94652 - 08/04/05 12:15 PM Re: Pool motor
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
The light circuit would be a better candidate for the receptacle but be aware of the "unspliced EGC" rule when you lay it out.
I pulled 2 EGCs when I did mine. The unspliced one went to the J box and another was used for the receptacle, switch etc.
My pump is 240v. I figure the I2R savings will pay for the extra few bucks I paid for the breaker ... eventually.
_________________________
Greg Fretwell
Top
#94653 - 08/04/05 12:37 PM Re: Pool motor
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
680.22 (A) (3) "Dwelling unit(s). Where a permanently installed pool is installed at a dwelling unit(s), no fewer than one 125 volt 15 or 20 ampere receptacle on a general purpose branch circuit shall be located not less than 3.0m (10ft) from, and not more than 6.0 m (20ft) from, the inside wall of the pool."

I would say a circuit for the pool motor is not a general purpose branch circuit, thus the convienience receptacle can not be fed from that circuit.
Top
#94654 - 08/04/05 01:58 PM Re: Pool motor
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
Branch Circuit, General-Purpose. A branch circuit that supplies two or more receptacles or outlets for lighting and appliances.

I suppose it all depends on if a pool pump is an "appliance" and if the light is "lighting".
They didn't have any problem with my receptacle on the same circuit as the wet niche light. (Lee Co Fla)
_________________________
Greg Fretwell
Top
#94655 - 08/04/05 02:25 PM Re: Pool motor
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
gfretwell, I don't understand the post about 2 equipment grounds and how that plays into line loss. I2R

Can you explain?


Dnk.....
Top
#94656 - 08/04/05 02:58 PM Re: Pool motor
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
With a 240v motor the loss in the wire will be less (increases with the square of current)
A wet niche light required an unspliced ground to the J box (with a few exceptions).
Since I was also feeding another circuit from this (the receptacles) it was easier to just pull 2 EGCs and avoid any confusion.
_________________________
Greg Fretwell
Top
#94657 - 08/04/05 03:11 PM Re: Pool motor
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Sorry, I didn't notice you switched topics in your post.

Somehow(I dunno),I thought you were suggesting an EGC had something to do with line loss.


Dnk......
Top
#94658 - 08/04/05 07:48 PM Re: Pool motor
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9037
Loc: Estero,Fl,usa
I will plead temporary insanity. I was digging in the yard and I was delerious when I came back in to post that. ;-)

Sorry for the confusion.
_________________________
Greg Fretwell
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals