#94619 - 08/03/05 05:07 PM Anti-shorts & MC cable
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I recently moved-on from my old job and started working for another contractor here in New Jersey. During one of our morning discussions/ ball-breaking sessions, it was brought up that anti-shorts (redheads) are no longer required for MC cable. It was news to me. When was this "change" made to the code? Personally, I think this is bad for the industry and could only lead to more ground/ neutral shorts and possibly start fires.

What do you think?

[This message has been edited by ShockMe77 (edited 08-03-2005).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#94620 - 08/03/05 06:10 PM Re: Anti-shorts & MC cable
Tiger Offline
Member
Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
My understanding is that it was never a requirement in the written language of the code, but may be a requirement in the manufacturer's specs (as they include several of them with the product).

Dave
Top
#94621 - 08/03/05 06:32 PM Re: Anti-shorts & MC cable
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Thanks Dave.

I'll bring that up next time it's discussed.

Makes sense to me!
Top
#94622 - 08/03/05 06:38 PM Re: Anti-shorts & MC cable
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Check out this thread,
http://electrical-contractor.net/ubb/Forum2/HTML/001320.html

the links are out of date, but Iwire provides the NEMA bulletin in his post of 11-27-2003 at 08:21 AM.

Roger

[This message has been edited by Roger (edited 08-03-2005).]
Top
#94623 - 08/03/05 09:31 PM Re: Anti-shorts & MC cable
Tiger Offline
Member
Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
Thanks for the clarification Roger. I finally looked up the difference between AC and MC. I'm using AC with the anti-short bushings.

Dave
Top
#94624 - 08/04/05 07:16 PM Re: Anti-shorts & MC cable
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Thanks Rog! I followed that link and read it all. I'm definitely going to still use the redheads just be on the safe side.

Ron
Top
#94625 - 08/06/05 11:51 AM Re: Anti-shorts & MC cable
poorboy Offline
Member
Registered: 06/02/05
Posts: 128
Loc: Central Maine
Followed the old thread, saw the comment about using a wrap of tape to secure them. I have stopped guys in the past from doing this because if you get enough tape on there the MC jacket is insulated from contact with the connector and remains unbonded. I had one guy doing ALL ends this way, meaning BOTH ends of a cable, leaving the jackets isolated.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 69 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals