#94574 - 08/01/05 12:12 PM #8 bonding wire
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Does the #8 solid ground that is used to bond the metallic frames of electric motors and associated parts of an indoor jacuzzi have to go back to the panel?

Or can it be bonded to the water supply to the jacuzzi?

I think it is the first option but i am not sure.
Thanks
Edward.
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#94575 - 08/01/05 01:52 PM Re: #8 bonding wire
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
It does not have to go back to the panel. You are just bonding all of the metallic parts together. You must connect the water lines to this. It is not optional.
Top
#94576 - 08/01/05 02:00 PM Re: #8 bonding wire
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
thank you
_________________________
Thanks
Edward
Top
#94577 - 08/02/05 06:15 PM Re: #8 bonding wire
foestauf Offline
Member
Registered: 08/01/05
Posts: 49
Loc: Florida
A guy other day was complaining to me that his inspector required him to run it back to panel.
Top
#94578 - 08/02/05 08:15 PM Re: #8 bonding wire
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
680.26 Bonding.
(A) Performance. The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed.
FPN:This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals