The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 78 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#9450 - 04/30/02 09:26 AM Table 8
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
What is the "coated" as in Uncoated vs. Coated Copper conductors referenced in table 8. The only thing I can think of is tinned conductors.
Anyone?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#9451 - 04/30/02 02:05 PM Re: Table 8
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Coated conductors are those you make relay coils, transformer windings, etc. out of. Normal conductors are uncoated, so use that table unless you're winding a relay.

Top
#9452 - 04/30/02 07:09 PM Re: Table 8
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks, George.

Top
#9453 - 04/30/02 07:28 PM Re: Table 8
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
To further the Q, what are they coated with? Varnish?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#9454 - 04/30/02 09:08 PM Re: Table 8
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Only you would ask that question Sparky.
Good on ya mate! Let me show my age, it used to be varnish, coils were finished in varnished cambric, the cambric being a linen cloth. I still mix my own when I wantsta builds one but when I tear up the sheets BOY does the missus get mad

They are made a LOT more resistant to heat by I'm sure some fancy polymer. Maybe some manufacturer is peering in, but may be unwilling to give up the company secret.

I guess my answer is: It used to be varnish, varnish works fine, a little hard to work with but they do use better stuff now.

BTW, Table 8 shows DC resistance, nice place to start but doesn't have a big basis in reality for AC calcs. You weren't wrong in your answer, but you were .05 ohms off.....shame on you.

[This message has been edited by George Corron (edited 05-01-2002).]

Top
#9455 - 05/01/02 09:44 AM Re: Table 8
WARREN1 Offline
Member

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
I guess I'm not smart, but if the conductor is coated with varnish or some other "polymer", then why is the resistance different? My Code instructor taught us that the coating was tin/nickel, therefore a change in resistance.

Top
#9456 - 05/01/02 10:19 AM Re: Table 8
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
tin/nickel is a coating, but a conductive one, you cannot have a conductive path, but an electromagnetic path. the varnish acts as an insulator so that the entire ball of copper may be used. Look at all the provisos under table 8. It is really a VERY general table, and due to change from manufacturer to manufacturer. Remember the first article of the code (OK up until 2002) "This code is not to be used as a design or specification guide" that's why.

Top
#9457 - 05/01/02 11:50 AM Re: Table 8
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
I still come across varnished cambric in the coils and transformers of some old radios. Quite a distinctive smell when one of these burns out.

We can still buy reels of enamelled wire for winding coils.


[This message has been edited by pauluk (edited 05-01-2002).]

Top
#9458 - 05/01/02 04:41 PM Re: Table 8
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Paul,
Yup, "If it don't smoke and glow, it ain't radio" is an old saying. Most of my ham stuff is digital, but when it comes to linear amplifier NOPE. I likes to see them 3-500Zs glow at me.

We can still buy it too, boy is it expensive, I have actually resorted to unwinding motors in a desparate act.

I had to rewind the coil for a 1957 BMW motor sickle not long ago, THAT was all varnished cambric.

Top
#9459 - 05/01/02 08:56 PM Re: Table 8
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
I'll try this from a bit earlier point of view. In NEC Ch.9 table 8, coated vs. uncoated refers to tin plating over copper. The difference in resistance comes from both types having the same OD, but tin is less conductive than copper. So why the tin in the first place? Used to be that rubber (like in RHH/RHW) had some sulfur compounds that would corrode bare copper. Tin would limit that problem. With modern polymers the sulfur is no longer of concern, but some wire like SIS is still tin plated.

[Table 430-149 for 2-phase motors still...1999 anyways.]

Top