#94448 - 07/30/05 04:34 AM O.R. Rooms
Surfinsparky Offline
Member
Registered: 07/29/05
Posts: 77
Loc: merritt island fl usa
I am an electrician for a small 250 bed hospital.I should say I am thee electrician for the hospital.Anyway we built a new facility 3 years ago.each O.R. suite has its own 120/208V 3 phase panelboard.There is no ground isolation, line isloation monitors or gfcis in the rooms.The rooms are anything but a dry location.The way I understand the code you must have gfcis and if you can't tolerate nuisance tripping you must have a ground isloation panel.Any clarity will help.
Top
2017 / 2014 NEC & Related Books and Study Guides
#94449 - 07/31/05 05:21 AM Re: O.R. Rooms
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Don, you are absolutly correct. In N.C. all O.R.'s must be supplied with Isolated Power systems so no problem here. I thought FL still mandated them as well. (guess I was wrong)

For an article from another frustrated Facilty Person on the Wet Location topic, click the link below.
http://www.healthcareengineering.net/archive/phile/Article.aspx?aid=192

And a little more information.
http://www.healthcareengineering.net/archive/phile/Article.aspx?aid=190


Roger



[This message has been edited by Roger (edited 07-31-2005).]
Top
#94450 - 07/31/05 06:45 AM Re: O.R. Rooms
Surfinsparky Offline
Member
Registered: 07/29/05
Posts: 77
Loc: merritt island fl usa
The way I see it it is an accident waiting to happen.I have found extension cords in buckets of water the staff was used to isolated power systems in our other facility.However they seem pretty clueless to the dangers.The only way I see how they got around A.H.C.A was they must have insisited they were only going to dry procedures.Then I still feel they at least need gfcis.The really odd thing is they are still grouding patients is this crazy or is it just me.If I mention my concerns to the chiefs they just think well it passed inspection so it must be right.I would like to install the right equipment but I feel it is a slippery slope does profit come before safety.I have been trying to correct this issue for some time.I don't really want to call it to inspectors attention if I can help it but if I am sure I am right on this and they don't cough up the cash to fix it.I almost feel obligated to do something about it.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 105 Guests and 18 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals