The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#9443 - 04/30/02 05:38 AM Drops from ceiling for machinery
Joe Carpenter Offline

Registered: 12/19/01
Posts: 55
Loc: USA
We are planning on moving some industrial machinery to a new location and re-install them. This will not be in a classified location. The electric drops from the ceiling to these machines are done in a variety of methods since they were installed by different techs over the years.
My question is, what is the preferred code compliant method? I have both 480 volts 3 phase and 208 volts single phase coming to each machine. Each machine draws a max of 20amps on the 480 and 10amps on the 208. Is Liquidtight Flexible Metal conduit attached to the side of 4" sq. boxes with 90 deg angle connectors w/strain relief OK? That way I could have all the conductors for both voltages inside and have one drop per machine. Or are flexible cords with strain relief the best method?,one drop cord for each voltage. I would like to set things up to have a neat appearance, and to be practical,and code compliant. I realize there are probably several different approved methods. i would like to hear how you like to do it.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#9444 - 04/30/02 05:43 AM Re: Drops from ceiling for machinery
EVAD7 Offline

Registered: 03/11/02
Posts: 37
Loc: MN
Cord drops would be the preferred method. Box on ceiling to kellem grip with twistlok device 6' 6" aff. Each voltage should be separate. Over 60amp we use pin and sleeve devices. Remember the cord can not be attached to any building surface unless it has strain relief.