The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
9 minutes 41 seconds ago
ESA Arc flash course
by frank
38 minutes 45 seconds ago
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
HotLine1 21
Webmaster 20
Trumpy 12
ghost307 12
frank 12
Who's Online
3 registered (Webmaster, Ruben Rocha, sparkyinak), 0 Guests and 197 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#9443 - 04/30/02 05:38 AM Drops from ceiling for machinery
Joe Carpenter Offline
Member

Registered: 12/19/01
Posts: 55
Loc: USA
We are planning on moving some industrial machinery to a new location and re-install them. This will not be in a classified location. The electric drops from the ceiling to these machines are done in a variety of methods since they were installed by different techs over the years.
My question is, what is the preferred code compliant method? I have both 480 volts 3 phase and 208 volts single phase coming to each machine. Each machine draws a max of 20amps on the 480 and 10amps on the 208. Is Liquidtight Flexible Metal conduit attached to the side of 4" sq. boxes with 90 deg angle connectors w/strain relief OK? That way I could have all the conductors for both voltages inside and have one drop per machine. Or are flexible cords with strain relief the best method?,one drop cord for each voltage. I would like to set things up to have a neat appearance, and to be practical,and code compliant. I realize there are probably several different approved methods. i would like to hear how you like to do it.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#9444 - 04/30/02 05:43 AM Re: Drops from ceiling for machinery
EVAD7 Offline
Member

Registered: 03/11/02
Posts: 37
Loc: MN
Cord drops would be the preferred method. Box on ceiling to kellem grip with twistlok device 6' 6" aff. Each voltage should be separate. Over 60amp we use pin and sleeve devices. Remember the cord can not be attached to any building surface unless it has strain relief.