The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
1 registered (mbhydro), 228 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94302 - 07/23/05 09:54 AM Panel from 600 amp service section.
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Doing a job in a commercial building with a 600 amp service section that has 2 - 100 amp panels and 1 - 200 amp panel there already. They are moving in machines and work tables I'll put drops in for.
I will probably need to add another 200 amp panel. Would that be considered a sub-panel? Do I need to isolate the neutrals and grounds in it? The other panels are not the bolt-in type breakers. I believe snap in breakers are ok for a commercial biulding, correct?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2014 / 2011 NEC & Related Books and Study Guides
#94303 - 07/23/05 01:35 PM Re: Panel from 600 amp service section.
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Is the new panel going to be supplied from (1)the existing panel or (2) connect directly to the utility company / service conductors ?
If (2) treat it as a service and label the main disconnect "Service Disconnect" (110.22) Number one of XX, no more than six.
If (1) it is a sub panel and label the main breaker "MAIN" (110.22)
In sub panels seperate in service panels bond.
Alan-- Inspector
Note. had the 1 & 2 reversed. It is correct now
[This message has been edited by Alan Nadon (edited 07-23-2005).]

[This message has been edited by Alan Nadon (edited 07-24-2005).]

[This message has been edited by Alan Nadon (edited 07-24-2005).]
_________________________
Alan--
If it was easy, anyone could do it.

Top
#94304 - 07/23/05 10:09 PM Re: Panel from 600 amp service section.
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
It'll be fed from the main service section with a shut off with 3 - 200 amp fuses.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#94305 - 07/24/05 07:57 AM Re: Panel from 600 amp service section.
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
The "shut off" with the three fuses is the service disconnect.
You write "with" not "from".
Is the shut off in the service or in the new panel ?
If in the service then it is the service disconnect and use four wire from there to the new panel. (2)
If in the new panel then the new panel is an additional service disconnect. (1)
*Note I got my 1 & 2 reversed in the last post I have edited it.
Alan--Inspector.
_________________________
Alan--
If it was easy, anyone could do it.

Top
#94306 - 07/24/05 09:58 AM Re: Panel from 600 amp service section.
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
The 200a shut off is in the service cabinet. I will get a 200a load center for the panel. The load center would be considered a sub-panel I believe, from the service section disconnect. So will probably have to isolate the neutrals and grounds.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#94307 - 07/25/05 07:40 AM Re: Panel from 600 amp service section.
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
The NEC does not address Bolt-in or Plug-on brekaers. The choice of breaker mounting style is strictly a design issue. that said, most specifications call for bolt-on breakers becuse that prevents contractors from installing "loadcenters" instead of "panelboards".

Note: neither the NEC nor UL consider loadcenters to be different from any other panelboard. the difference in the panels is strictly a tradition not a standard. Think 4x4 pickup versus a 1/2 ton. It comes down to personal preference and available options only.

Top
#94308 - 07/25/05 11:55 AM Re: Panel from 600 amp service section.
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
 Quote:
Note: neither the NEC nor UL consider loadcenters to be different from any other panelboard. the difference in the panels is strictly a tradition not a standard. Think 4x4 pickup versus a 1/2 ton. It comes down to personal preference and available options only.


Wouldn't the short circuit ratings be higher on a panelboard? Most of the ones I run into in cinema work are. A lot are also "Series Rated" for fault current management.

I wouldn't want a resi loadcenter in one site I work at. The theatre is literally right on top of a network distribution transformer! A short in the projector's maint. receptacle took out the 225 amp subpanel breaker with a nice loud bang! (It tripped, didn't explode.) That same fault would've probably rearranged the buss bars on a loadcenter!
_________________________
Stupid should be painful.

Top
#94309 - 07/25/05 10:07 PM Re: Panel from 600 amp service section.
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Nor sure I see the difference between a load center and a panelboard. What article in the code book shows the size of ground wire for the 200 amp panel? Should be # 6.
_________________________
The Golden Rule - "The man with the gold makes the rule"