The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94204 - 07/17/05 08:31 AM h20 heaters
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
a friend asked me if a 125 amp sub panel would be ok for three water heaters that are 40 amps each.

Top
2014 / 2011 NEC & Related Books and Study Guides
#94205 - 07/17/05 08:51 AM Re: h20 heaters
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Is the 40 amps the actual heater current, or the individual circuit ratings?
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#94206 - 07/17/05 08:56 AM Re: h20 heaters
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
individual circuit ratings

Top
#94207 - 07/17/05 09:30 AM Re: h20 heaters
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Really comes down to the application.

If you're talking about water heaters used as household ones are....heating separate systems, and used occasionally for brief periods, the 125 amp panel should be fine.

If these are used together, as in supplying hot water to a production process, and use continuously, than you have to treat the loads as continuous, and have that 25% "buffer' added in to both your panel and the wire supplying it.
(Use the KW ratings of the heaters for your calcs).

Top
#94208 - 07/17/05 03:24 PM Re: h20 heaters
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
At max proper circuit loading, which would be (40a. x 80%) 32a. each, that's 96 a. total.

Another way, 3 x 40a. = 120a. Either way, you're okay.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com