The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 256 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94107 - 07/06/05 03:04 PM sub panel without equipment ground?
royta Offline
Member

Registered: 09/03/04
Posts: 136
Loc: CA
A customer has a sub-panel on an the inside of an exterior wall of a barn type building. I need to remove this panel and install a new panel on the other side of the wall (outside of the building). I guess that doesn't really matter to you.

Here's my situation. There is a meter/main combo on the side of the house which feeds a sub-panel located in the house. The main panel also fed a 240V branch circuit going to a disconnect located at the back of the house. Somebody before me removed the interior of the disconnect and used it as a junction box to feed the same sub-panel I am trying to relocate. Here's the problem, there is no equipment ground between the main and sub-panel. There are only two 120V legs and a Neutral between the two panels. For ground at the sub-panel, there is a grounding electrode. I am trying to squeeze under 2002 NEC 250.32(B)(2) and bond the neutral bar to the sub-panel can. It would be easy to pull an equipment ground between the junction box and the sub-panel, however it won't be so easy to get a ground between the junction box and the main panel (both are on exterior walls of the house). I qualify under parts 1 & 2 of the Article, but part 3 seems to catch me. Where...ground-fault protection of equipment has not been installed on the common ac service. Since this is a residential installation, there is obviously ground-fault protection located somewhere in the house. However, it is not coming from the main panel, only the sub-panel located in the house. Does this still fall under the "common ac service"? Besides this, the junction box (old disconnect), contains splices of the current carrying conductors feeding the barn sub-panel.

What can I legally get away with?

Top
2014 / 2011 NEC & Related Books and Study Guides
#94108 - 07/06/05 07:12 PM Re: sub panel without equipment ground?
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I am not sure about the exact wording here, which _might_ cause problems if there are GFCIs on branch circuits. However, as far as the _reason_ for part 3 of this article, GFCIs on branch circuits are not relevant.

The issue is ground fault detection on the entire service. A bond between neutral and ground at the subpanel would be a connection between circuit conductors and ground downstream of this ground fault detection. Depending upon how the ground fault detection is implemented, such a bond could desensitize the ground fault detection or could cause false tripping.

I rather doubt that this residence has service ground fault protection

-Jon

Top
#94109 - 07/06/05 07:15 PM Re: sub panel without equipment ground?
royta Offline
Member

Registered: 09/03/04
Posts: 136
Loc: CA
Excellent. It looks like I go back tomorrow and finish the job. Thanks.

Roy


edit -- How do I bond the junction box? Do I attach the Neutral to it?

[This message has been edited by royta (edited 07-06-2005).]

Top
#94110 - 07/06/05 08:46 PM Re: sub panel without equipment ground?
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
It sounds to me like the 'junction box' is on the side of the building with the service. Since 250.32(B)(2) applies to _detached_ structures, it seems to me like you would have to run an equipment ground to the junction box...which on re-reading your original post seems to be the problem.

Remember that the only time you can run a subpanel like a 'service' with bonded ground and neutral is if the subpanel is in a detached structure with no metallic pathways between the two structures.

-Jon