#94041 - 07/02/05 08:37 PM Is a screeen cage a permanent barrier?
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
In reference to the electrical elements of a pool, is a screen cage a permanent barrier.
examples;
Can a receptacle outside the cage, 11 feet from the pool, be counted as the required one?
If it is only 4 feet from the pool but outside the screen is it OK?
_________________________
Greg Fretwell
Top
2017 / 2014 NEC & Related Books and Study Guides
#94042 - 07/03/05 02:34 AM Re: Is a screeen cage a permanent barrier?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Well Greg, I would make the call that the receptacle located 4 feet from the pool has to go and the receptacle located 11 feet from the pool meets the requirement of 680.22(A)(3). I am making that call based on 680.22(A)(6) and based on the fact that one can "pierce" the screen cage

Some times we have to put on the hat of King Solomon.
_________________________
George Little
Top
#94043 - 07/03/05 05:07 AM Re: Is a screeen cage a permanent barrier?
drummer too Offline
Member
Registered: 06/18/05
Posts: 12
Loc: Spring Hill, Florida, USA
I would think the screen would be a permanent barrier. We are know required to supply, at back of house, a receptacle inside and outside of cage. AHJ says the required back outlet inside of screen is not accessable to the rest of outside. If they require an outlet inside and outside of screen enclosure because of accessability, then the screen would be considered a barrier. Plus it's not considered the required within 20 foot rule if outside the screen enclosure.
I laugh at the requirement of a receptacle within 20 foot of pool, but greater than 10 foot, unless physically impossible to keep 10 foot (680.22 A.4)than 5 foot or greater is OK. Why require an outlet and potential hazard with (680.22 A.3). Swim at your own risk!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals