The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#94027 - 07/01/05 10:51 AM Rebar Bonding on Pool
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Well this one will get you thinking

Contractor uses an "Acorn" clamp- the type of clamp you use to terminate a GEC on a ground rod, to secure the #8 solid to the rebar of a pool. So the question is: can he fold the #8 over and not cut it and slip it in between the rebar and the clamp? Is this considered 2 wires now? We all agree that this type of clamp is only Listed for one wire. Secondly, is this clamp suitable for rebar? I have been approving this type of connection for years and now it appears I could be in error.

As the attorney said-"What say you?"
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#94028 - 07/01/05 05:54 PM Re: Rebar Bonding on Pool
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Clamps approved for direct burial are also approved for concrete encasement (see the UL White Book "KDER"). i don't see anything in the UL listing that would prohibit the use of an acorn clamp to rebar if the clamp was correctly sized.

IMO, bending the wire over is going to have to be a judgement call on your part, though I don't see why this would need to be done.

A question for you. If someone hammered in a piece of 5/8" rebar as a grounding electrode, would you accept this per 250.52(5)(b)? If you did accept this, would you require a special "rebar" clamp or would an acorn do the job?

Personally, unless someone can come up with something really compelling, I'd continue to accept the acorn clamp that is listed & marked for direct burial. I think your years of experiance in this area are correct. I'm also sure that if I'm wrong, someone will kindly point out the error of my ways.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#94029 - 07/01/05 09:04 PM Re: Rebar Bonding on Pool
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
George I vote it is still one wire. The reason we worry about multiple wires in a terminal not rated for it, is one may be getting all the pressure and the other still loose.
_________________________
Greg Fretwell

Top
#94030 - 07/02/05 06:42 AM Re: Rebar Bonding on Pool
JG Offline
Member

Registered: 03/24/04
Posts: 16
It is not allowed in NM: Cu to FE in direct contact: Art 110

Top
#94031 - 07/02/05 11:37 AM Re: Rebar Bonding on Pool
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
JG- Would you mind explaining your abbreviations? And Code reference beyond the Article number? Thanks.

NM = New Mexico?
Cu = Copper?
FE = ?
Art 110 = Maybe 110.14?
_________________________
George Little

Top
#94032 - 07/02/05 06:43 PM Re: Rebar Bonding on Pool
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Grorge I would not like a #5 rebar ground rod but I think I would have to just talk them out of it or 90-4 them.
250.52(A)(5) doesn't seem to prohibit it.

(b) Electrodes of rods of iron or steel shall be at least 15.87 mm (5/8 in.) in diameter. Stainless steel rods less than 16 mm (5/8 in.) in diameter, nonferrous rods, or their equivalent shall be listed and shall not be less than 13 mm (1/2 in.) in diameter.

There are lots of acorns listed for rebar
_________________________
Greg Fretwell

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals