#93995 - 06/26/05 02:30 PM ENT in plenum ceiling
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
ENT in a plenum ceiling where the ceiling is suspended hat channel with sheetrock. In a high rise that is fully sprinkled per NFPA13-1999 and is used as a residence. What say you?
Top
2017 / 2014 NEC & Related Books and Study Guides
#93996 - 06/26/05 05:37 PM Re: ENT in plenum ceiling
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Look at 300.22(C)(1).
_________________________
Don(resqcapt19)
Top
#93997 - 06/26/05 08:28 PM Re: ENT in plenum ceiling
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Thanks. Sometimes you just can't find stuff in the code book even when you've seen it a million times.