#93908 - 06/23/05 01:17 PM Hallway Outlet Requirement (210.52H)
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
This house has a walkway 36 inches wide , 12 feet long with railings (open) both sides. Open to floor 10 ft dn also both sides. Since nothing can ever be placed in this area. ???? Outlet required ????Owner says its a Balcony not hallway.
Top
2017 / 2014 NEC & Related Books and Study Guides
#93909 - 06/23/05 03:26 PM Re: Hallway Outlet Requirement (210.52H)
Tiger Offline
Member
Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
I don't find a definition for hallway in the 2002 or 2005 NEC. What does the AHJ call it?

Dave
Top
#93910 - 06/23/05 04:27 PM Re: Hallway Outlet Requirement (210.52H)
HLCbuild Offline
Member
Registered: 12/05/04
Posts: 206
Loc: Herndon,Va USA
In the building side of things, balconies are cantilevered without support on the cantilevered overhang. Sounds like a hallway to me. And even though nothing is placed in this "area" someone might want to plug in a vacuum.
Top
#93911 - 06/23/05 05:35 PM Re: Hallway Outlet Requirement (210.52H)
e57 Offline
Member
Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
You could stick a floor outlet on your "Bridge", if need be.

Or maybe its a "Cat-walk"? (I like the sound of that!)

Other than that, is seems that it still counts as "wall-space".

Quote:
210.52(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers such as freestanding bar-type counters or railings


So if you call it a "hallway", you would need one. If not you might need 2-4...

Give your Inspector a call and see what he wants to call it.

I have had to put recepts along a circular interior "Balcony", because it was "wall space". I went back a year or so later, and figured they would never be used. Go figure there was a floor lamp in every one.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#93912 - 06/26/05 08:51 PM Re: Hallway Outlet Requirement (210.52H)
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Quote:
Go figure there was a floor lamp in every one.
"If you build it, they will come!"
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#93913 - 06/26/05 11:05 PM Re: Hallway Outlet Requirement (210.52H)
e57 Offline
Member
Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
LOL
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#93914 - 06/27/05 12:50 PM Re: Hallway Outlet Requirement (210.52H)
wa2ise Offline
Member
Registered: 11/29/02
Posts: 773
Loc: Oradell NJ USA
If you put outlets at both ends of that walkway (balcony/hall) then everywhere in that walkway is within 6 feet of an outlet (if it's 12 feet long), yes?
Top
#93915 - 06/27/05 09:11 PM Re: Hallway Outlet Requirement (210.52H)
georgestolz Offline
Member
Registered: 06/26/05
Posts: 90
Loc: Fort Collins, CO, US
Careful: Hallways do not fall under the 6' / 12' rule.

I'd put an outlet on either end of the hallway, or just one on one end. 210.52(H) will be satisfied.
_________________________
-George
Top
#93916 - 06/28/05 11:38 AM Re: Hallway Outlet Requirement (210.52H)
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
10 ft (OR MORE) so a hallway 15ft as such would require one outlet placed anywhere within that 15 ft. The way it reads. So if the walkway or (Hallway) extends even one ft. over on either side of that 12 ft. it would still be part of the hallway and the outlet would be legal placed there.Thats the way I read it. It does not state where in that over 10ft. hallway the outlet is required to be placed.
Top
#93917 - 06/28/05 06:48 PM Re: Hallway Outlet Requirement (210.52H)
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Agreed. Even a 100' hallway would require only one receptacle, although I'd consider a couple more with vacuum-cleaner cord length in mind if it were my job.

I don't consider a catwalk to be a hallway. We recently did a large (over 7500 sq ft) house with a catwalk wide enough for a table; no receptacle needed.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 79 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals