#93835 - 06/19/05 11:58 AM Running Conduit in bar joist
artex Offline
Junior Member
Registered: 06/16/05
Posts: 1
Loc: texarkana, AR,usa
The 1996 code changed the strapping requirement for conduits, IMC,RD,EMT.
The code allows the conduits to be supported by the framing members, but are not required to be rigidly supported, except at the boxes.
Our inspector says the handbook picture shows the conduit in a bar joist, in the "V" of the bar joist so the conduit cannot move. I said that is a good installation but that the code does not require that the conduit be place so it will not move. The exception is the strapping at the boxes or temination point.
What is your interpretaion?
Top
2017 / 2014 NEC & Related Books and Study Guides
#93836 - 06/19/05 12:03 PM Re: Running Conduit in bar joist
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
That is allowed in my area, we do it often.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#93837 - 06/27/05 05:28 AM Re: Running Conduit in bar joist
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
358.30 2002 refers to Securing And supporting. 358.30 b again refers to Securly Fastened.Hand book refers to 342.30b (4)in handbook for Commentary. I;d say can be run any area in bar joists but must be straped per code requirements.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals